Doing some testing today on a Wet Room installation.
Fed from its own small CU. And consists of
2 x seperate 50A (for 10.5kw shower) circuits
1 x 20a radial for underfloor heating. This runs direct from CU to a fused spur and then from the fused spur to the UFH controller.
1 x 20a radial for 2 x sockets in a storage cupboard and a fused spur from this for the heated towel rail.
1 x 6a light circuit.
Everything fine until I got to the L-N IR test. It kept giving me a reading fluctuating between 0.08 & 0.37 MOhms. L-E and N-E just fine.
Nothing is going bang as it would with a L-N dead short. So it’s not that.
The 2 fused spurs have neons as do the 2 pull cords for the showers All of these I ensured were switched off as I know neons can cause an issue.
However this didn’t solve the issue on the global IR and I’m scratching my head.
The board is a Fusebox RCBO board. I tried doing the test on the supply side of each RCBO to see if that made a difference. But it didn’t.
I thought it may be the UFH controller so I disconnected that completely yet still got the same problem.
I have traced every single cable as it is still at the first fix stage. Sockets etc have just been added as the plasterer and tilers etc aren’t in for another month. Nothing is damaged. All the connections are sound and terminated correctly in the sockets and spurs, the shower cables have a wago on each conductor and are taped up. Towel rail isn’t yet connected but the supply cable is terminated in the fused spur.
What I can’t work out is why every single circuit is being affected by whatever is causing this fault.
Anyone ever experienced this? I could understand one circuit having the issue, but not every circuit.