I always think that a requirement to disconnect something for an IR test is a sign of cheap or poor design. Clearly it is possible to make devices that don't need to be disconnected and unnecessary fiddling around with cables leads to wear and tear, errors and the possibility of introducing faults that the test was supposed to detect.

There are two aspects - whether the device will spoil the test result and whether it will be damaged. Anything that is connected to the mains can expect to see an RMS voltage of 253V and hence a peak voltage of 358V continuously for decades. Film caps ought to withstand 500V or else they are not fit for a noisy environment that can see spikes of a few kV. VDRs will give spurious test results but won't be readily damaged by the current-limited output of the IR tester. The weakest links would likely be 400V electrolytics and transistors in SMPSUs, but I don't like electrolytic capacitors hard-wired into my electrical installation e.g. in sockets with USB ports.

Back in the days of big, tough stud-mounted thyristors in theatre lighting dimmers, there would often be notices on the dimmer modules warning not to carry out insulation tests. Even if the thyristors were rated for 800PIV and the suppression capacitors 500V DC, and the primary of the mains transformer would thwart any attempt to test L-N with a resistance of only a few hundred ohms, the warnings would be there.
 
I was fitting Hager ones yesterday and they have a little sticker on them saying you can IR test at the outgoing terminals....
I thought that was great when I first saw those stickers, until I realised you still have to disconnect the neutral as it is still connected through when the RCBO is off. Apparently Wylex now do compact 1 module RCBOs with 2 pole switching where you can test without disconnecting.
 
I thought that was great when I first saw those stickers, until I realised you still have to disconnect the neutral as it is still connected through when the RCBO is off. Apparently Wylex now do compact 1 module RCBOs with 2 pole switching where you can test without disconnecting.
Fusebox do 1 module mini RCBO which are DP.

I normally fit those which is why I think I’ve not normally had an issue. However on this job they were SP.

Just need to remember to read the instructions in future. 😂
 
I always think that a requirement to disconnect something for an IR test is a sign of cheap or poor design. Clearly it is possible to make devices that don't need to be disconnected and unnecessary fiddling around with cables leads to wear and tear, errors and the possibility of introducing faults that the test was supposed to detect.

There are two aspects - whether the device will spoil the test result and whether it will be damaged. Anything that is connected to the mains can expect to see an RMS voltage of 253V and hence a peak voltage of 358V continuously for decades. Film caps ought to withstand 500V or else they are not fit for a noisy environment that can see spikes of a few kV. VDRs will give spurious test results but won't be readily damaged by the current-limited output of the IR tester. The weakest links would likely be 400V electrolytics and transistors in SMPSUs, but I don't like electrolytic capacitors hard-wired into my electrical installation e.g. in sockets with USB ports.

Back in the days of big, tough stud-mounted thyristors in theatre lighting dimmers, there would often be notices on the dimmer modules warning not to carry out insulation tests. Even if the thyristors were rated for 800PIV and the suppression capacitors 500V DC, and the primary of the mains transformer would thwart any attempt to test L-N with a resistance of only a few hundred ohms, the warnings would be there.
It's all down to some little china man selling them the pcb's fully loaded for a £2.00 a go
Oh and we do cases btw for £2.00 with your logo
 

Reply to Odd problem on IR Test. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
625
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
463
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
578
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
732
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
616

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock