Been back today. Turns out to be 2 of the RCBOs.
With all circuits disconnected from RCBO they all get the expected >999 Mohm across L-N
The 2 x 20A RCBO however give a reading of 0.08Mohm, even with the conductors removed. The 2x 50A & 1x 6A don’t. 🤷🏼‍♂️
So I’m going to speak to Fusebox on Monday and ask why. I could see 1 being a faulty one. But 2 and from the same supplier so likely the same batch. It’s odd that they would give that reading.
have you checked the instructions do not forbid insulation testing?
Doing some testing today on a Wet Room installation.
Fed from its own small CU. And consists of
2 x seperate 50A (for 10.5kw shower) circuits
1 x 20a radial for underfloor heating. This runs direct from CU to a fused spur and then from the fused spur to the UFH controller.
1 x 20a radial for 2 x sockets in a storage cupboard and a fused spur from this for the heated towel rail.
1 x 6a light circuit.
Everything fine until I got to the L-N IR test. It kept giving me a reading fluctuating between 0.08 & 0.37 MOhms. L-E and N-E just fine.
Nothing is going bang as it would with a L-N dead short. So it’s not that.
The 2 fused spurs have neons as do the 2 pull cords for the showers All of these I ensured were switched off as I know neons can cause an issue.
However this didn’t solve the issue on the global IR and I’m scratching my head.
The board is a Fusebox RCBO board. I tried doing the test on the supply side of each RCBO to see if that made a difference. But it didn’t.
I thought it may be the UFH controller so I disconnected that completely yet still got the same problem.
I have traced every single cable as it is still at the first fix stage. Sockets etc have just been added as the plasterer and tilers etc aren’t in for another month. Nothing is damaged. All the connections are sound and terminated correctly in the sockets and spurs, the shower cables have a wago on each conductor and are taped up. Towel rail isn’t yet connected but the supply cable is terminated in the fused spur.
What I can’t work out is why every single circuit is being affected by whatever is causing this fault.
Anyone ever experienced this? I could understand one circuit having the issue, but not every circuit.
My guess would be that L-N IR dc test damaged the rcbos internal circuitry
If it makes you feel any better I managed to kill a freezer once doing a global IR test. For EICRs and board changes I stick to L+N to E!
I was fitting Hager ones yesterday and they have a little sticker on them saying you can IR test at the outgoing terminals....
So thanks for reminding us to check the instructions.
I always think that a requirement to disconnect something for an IR test is a sign of cheap or poor design. Clearly it is possible to make devices that don't need to be disconnected and unnecessary fiddling around with cables leads to wear and tear, errors and the possibility of introducing faults that the test was supposed to detect.
There are two aspects - whether the device will spoil the test result and whether it will be damaged. Anything that is connected to the mains can expect to see an RMS voltage of 253V and hence a peak voltage of 358V continuously for decades. Film caps ought to withstand 500V or else they are not fit for a noisy environment that can see spikes of a few kV. VDRs will give spurious test results but won't be readily damaged by the current-limited output of the IR tester. The weakest links would likely be 400V electrolytics and transistors in SMPSUs, but I don't like electrolytic capacitors hard-wired into my electrical installation e.g. in sockets with USB ports.
Back in the days of big, tough stud-mounted thyristors in theatre lighting dimmers, there would often be notices on the dimmer modules warning not to carry out insulation tests. Even if the thyristors were rated for 800PIV and the suppression capacitors 500V DC, and the primary of the mains transformer would thwart any attempt to test L-N with a resistance of only a few hundred ohms, the warnings would be there.
I thought that was great when I first saw those stickers, until I realised you still have to disconnect the neutral as it is still connected through when the RCBO is off. Apparently Wylex now do compact 1 module RCBOs with 2 pole switching where you can test without disconnecting.
Fusebox do 1 module mini RCBO which are DP.
I normally fit those which is why I think I’ve not normally had an issue. However on this job they were SP.
Just need to remember to read the instructions in future. 😂
It's all down to some little china man selling them the pcb's fully loaded for a £2.00 a go
Oh and we do cases btw for £2.00 with your logo