have you checked the instructions do not forbid insulation testing?Been back today. Turns out to be 2 of the RCBOs.
With all circuits disconnected from RCBO they all get the expected >999 Mohm across L-N
The 2 x 20A RCBO however give a reading of 0.08Mohm, even with the conductors removed. The 2x 50A & 1x 6A don’t.
So I’m going to speak to Fusebox on Monday and ask why. I could see 1 being a faulty one. But 2 and from the same supplier so likely the same batch. It’s odd that they would give that reading.