At least in the UK (and possibly ROI) the use of IT supplies and insulation monitoring are only for skilled supervised systems where faults are very likely to be detected and corrected in a timely manner. The usual use-cases include ship electrics and operating theatres where you really don't want avoidable trips on a first-fault.Ironically I have just received an instruction manuel from the dealer(PRAMAC supplier).Until now I have not had any of my emails replied to as their technical helpline has been "under maintenance".The instructions state that an "insulation monitor" is available if an IT configuration is preferred.Had,nt expected that.Instructions also provide a UK website which I will contact to get their input into my concerns.As always the input from the forum is much appreciated.
PRAMAC seems to be a decent company and they do offer LPG generators that have some advantages for backup (long life of stored fuel, difficulty of stealing it if in a fixed tank) so I would hope they could offer you a better arrangement.
Modifying one to have the CPC back to the generator and RCD there is possible but probably an issue for warranty, etc.
In our case we needed a 3-phase generator in a relative hurry (for winter, not in 8-10 weeks lead time on new builds seen just now) and we asked Stephill Generators and they were happy to modify an in-stock model that had sockets to put a 100mA delay RCD on the 400V circuit to suit our hard-wired use. However, making it floating-chassis to mitigate open-PEN risks might not be practical if the AVR is referenced in any way to the 12V DC system that is always to the metalwork due to typical internal combustion engine electrics.
A final option you could consider is one of the open-PEN units for EV support, but you would need to consider how it is connected as probably it has to be powered from the generator and so would need to be 'reset' on start-up and that would make any automatic start/change-over tricky.