Yes.Similar to UKI'm guessing this is in ROI and I'm aware that there is a "neutralising link" between the supplier's PEN and the local earth rod, etc. However, is it a bit like UK TN-C-S where the N & E are only ever linked in the supply cut-out,
I,ve been a supporter of this approach for a long time.This idea would (in my experience)..The reason for asking is the time you need to use a generator is under supply fault conditions and that could well include the open-PEN situation, so if any transfer switch could be isolating the supply PEN and line, leaving the installation on the earth rod and then the generator would also be safe under open-PEN failure of the supply.
..solve 100% of open PEN issues in new housing estates
..95% in rural houses
..very large numbers of urban houses.The remainder could have their metallic services rendered "harmless"by installing plastic inserts at the point they enter a home.
I should add that if I was doing this genny install in the UK ,I would feel less concerned.From reading this forum I understand that many of your TNC-S supplies are converted TNC underground supplies.I would consider those significantly safer than overhead supplies.
Secondly, I would imagine that the lead sheath ( or what remains of it after conversion to TNC-S.) would still provide a great earth rod.This should be very effective in dragging down the "touch voltage" occuring during any fault.