Via conduit.How would the proposed NYY-J replacement be routed back to that consumer unit?
You make a good point, I wondered that after I wrote it.Slightly off topic but this has intrigued me for ages, you state "B32 possibly feeding two radials" as that's what it looks like but I don't believe that device has any over current protection at all, its just an RCD with contacts rated to 32A just like the 63A and 80A RCD's we so often see in consumer units.
Galv conduit would certainly provide good mechanical protection. @timhoward raises the issue of CCC - I don't know the differences between SWA and NYY off the top of my head, nor the correction factor when enclosed in conduit, but you may need to increase cable size and also that of the conduit. Seems like quite a bit of additional cost for something that isn't known to be faulty.Via conduit.
I had the same problem a few months ago, my mate was looking at some wiring in a food wagon and he rang me for advice on what to do next, he says there is a 32A RCD protecting the installation without any breakers and I said well if its a 32A RCD then it must be an RCBO so its covered but he was adamant it was just an RCD, when he sent me a picture and I looked a bit closer it dawned on me that it was indeed just an RCD.You make a good point, I wondered that after I wrote it.
So it isn't working because it has been disconnected?
If it said 63A or 80A etc the you would automatically assume its just an RCD without any other protection, its just the fact that it has a low value on it that I think loads of people will think its an MCB as well, same as the 20A and 25A ones that are also knocking about. Just doesn't make any sense to me to have all that different tooling to make different rated RCD's when a 100A would cover everything, the cost on saved metal must be minuscule.
Not the outcome I'd been expecting.So it isn't working because it has been disconnected?
I suppose everything has a price point. It could be quite a bit more expensive overall to manufacture a 100A rated RCD compared to a 25AI had the same problem a few months ago, my mate was looking at some wiring in a food wagon and he rang me for advice on what to do next, he says there is a 32A RCD protecting the installation without any breakers and I said well if its a 32A RCD then it must be an RCBO so its covered but he was adamant it was just an RCD, when he sent me a picture and I looked a bit closer it dawned on me that it was indeed just an RCD.
Other than having been disconnected is there anything wrong with the existing cable?With that now the culprit. I’ve ordered a vent plug for the Wiska Box. Some Wago 222 Connectors and something to connect the Wiska Box and RCD enclosure.
In hindsight singles would probably be better but I’ve got 30m of NYY and the price of cable and also selling the NYY.
Why are you going to replace the cable?
Are you going to reconnect it?