I could be wrong, but have a funny feeling that regulations in IE require that 3 pole isolation is used and neutral shouldn't be broken. Perhaps this only applies to the main isolator or perhaps it doesn't apply at all...
should never break a neutral via a switch , if it hangs you can end up with 400 volts on a 230 volt circuit which will cause havoc.
 
should never break a neutral via a switch , if it hangs you can end up with 400 volts on a 230 volt circuit which will cause havoc.
On a TT you need to isolate all conductors including the neutral, hence the switch where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.
 
should never break a neutral via a switch , if it hangs you can end up with 400 volts on a 230 volt circuit which will cause havoc.

I'd agree where functional switching is concerned, but isolators are manufactured for a specific purpose and to specific standards - there should be no danger of any live conductor 'hanging'.
 
TT (Direct) Earthing is essentially non-existant within the State, bar perhaps a very few relics. TN-C-S (Neutralised) applies to very nearly 100% of electrical installations.
No caravan parks, swimming pools, stables etc ? That would use TT earthing ?.
 
4 pole main switches are fairly common here, but the point was more about the fact we're free to use them, whereas I believe they can not be used in IE.

I wouldn't say free to use, you would only switch the neutral when absolutely necessary.
Switching the neutral introduces a greater risk of losing the neutral to the load whilst the phases are still connected thus damaging the load.
 
I'd agree where functional switching is concerned, but isolators are manufactured for a specific purpose and to specific standards - there should be no danger of any live conductor 'hanging'.

There is always a non-zero chance of a fault happening.

And why would you need to switch the neutral on a TN supply?
 
There is always a non-zero chance of a fault happening.

And why would you need to switch the neutral on a TN supply?

That's part of the reason why I'm raising this point. I'm under the impression that it isn't permitted in IE, where the vast majority of supplies are TNC-S, but I see plenty of 4 pole isolation on TN supplies in the UK.

I have questions to ask which expand on this and don't wish to hi-jack the OP's thread more than has already happened. It's not a subject I've seen under much discussion on the forum, so have started a thread and would welcome any input.

 
That's part of the reason why I'm raising this point. I'm under the impression that it isn't permitted in IE, where the vast majority of supplies are TNC-S, but I see plenty of 4 pole isolation on TN supplies in the UK.

I have noticed a trend towards installing 4 pole main switches where until a few years ago 3 pole would always have been preferred.
 
On a TT you need to isolate all conductors including the neutral, hence the switch where the neutral contact is set back so it closes early and breaks late, relative to the 3 phases.
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for us sparks to discuss for sure.
 