Hi All,
I appreciate the post about providing advice to DIYers, but I always treble check, at least, anything I do and won’t flout the law.
But I’m struggling to find a definitive answer to this. If you have a cable running over a garden, a cable that is waterproof, like a pond cable, how can you protect it from any damage? I don’t mean how do you protect it from getting damaged, but protecting from every possible type of short or open circuit.
Let’s say it degrades, or is chewed by an animal, what protects it from every scenario. That is live to earth, neutral to earth or any variant.
I ask because I read conflicting info that an RCD only protects live to earth!?
Will a fused inline RCD not protect from all scenarios?
Thanks.
 
an rcd measure for imbalance between live and neutral... the "30mA" that is stamped on them.
If the current isn't the same between the live and neutral, then it must be escaping somewhere... ie, to Earth... and possibly via through someone's body

The term "double pole" RCD means that it actually switches off both live and neutral... otherwise, it may not actually switch off both sides.

An RCD does not however, protect from overcurrent (overload)... tht is where a fuse or circuit breaker (mcb) comes in.

An RCBO, fitted in the consumer unit, combines the features of both rcd and mcb


Any cable should be suitable for the environment.... so mechanical protection "as far as is reasonably practicable" so something like armoured cable for the majority of the run, then jointed to flex for the last short bit.... Depending what you're supplying.

Using plain flex for the entirety of a cable run just means it is more likely to get damaged.... and you wouldn't know where
 
an rcd measure for imbalance between live and neutral... the "30mA" that is stamped on them.
If the current isn't the same between the live and neutral, then it must be escaping somewhere... ie, to Earth... and possibly via through someone's body

The term "double pole" RCD means that it actually switches off both live and neutral... otherwise, it may not actually switch off both sides.

An RCD does not however, protect from overcurrent (overload)... tht is where a fuse or circuit breaker (mcb) comes in.

An RCBO, fitted in the consumer unit, combines the features of both rcd and mcb


Any cable should be suitable for the environment.... so mechanical protection "as far as is reasonably practicable" so something like armoured cable for the majority of the run, then jointed to flex for the last short bit.... Depending what you're supplying.

Using plain flex for the entirety of a cable run just means it is more likely to get damaged.... and you wouldn't know where
Many thanks for this. I had read about RCBO and hoped to find a waterproof one I could put outside, due to my ‘consumer’ unit being from the good old days…IMG_0667.jpeg
 
Last edited by a moderator:
that cant be right... all only 30A?

should have white spot for 5A for light.... blue for 15A for an immersion heater maybe??


Anyway.... its well past its use by date.
 
Ah, that was just from online. Couldn’t take a picture of mine, the cat was on my lap 😊
I know it doesn’t meet ‘current regs’, but still legal, as far as I am aware, therefore no need to change for change sake.
 
Well… just for completeness 😊 here’s my fuse box, a notice hanging up in the fuse cupboard which was here when we moved in; I think it must be 2025 European regs…….
Annnd my cat.

Added.. Just noticed that sign says for Women!!! I can guess the age of that poster!
 

Attachments

  • IMG_2025-12-17-083315.jpeg
    IMG_2025-12-17-083315.jpeg
    202.9 KB · Views: 42
  • IMG_2025-12-17-083334.jpeg
    IMG_2025-12-17-083334.jpeg
    367.3 KB · Views: 40
  • IMG_2025-12-17-083352.jpeg
    IMG_2025-12-17-083352.jpeg
    195 KB · Views: 41
Dating the sign… which is amazing to have one in near good condition…

It was when “ring” circuits were a new idea.

The sign is “for women”… so was the house women’s refuge or something at one time? Where there wasn’t a man about the house to deal with it? ( I’m being sarcastic, not sexist)

A London phone number with only 4 digits?
40’s or 50’s at a guess.


Oh…. And what time did they think it was right to cook babies in the “baby cooker”??
 
Dating the sign… which is amazing to have one in near good condition…

It was when “ring” circuits were a new idea.

The sign is “for women”… so was the house women’s refuge or something at one time? Where there wasn’t a man about the house to deal with it? ( I’m being sarcastic, not sexist)

A London phone number with only 4 digits?
40’s or 50’s at a guess.


Oh…. And what time did they think it was right to cook babies in the “baby cooker”??
4375212 is a 7 digit number up until 1990
 
For you historians out there, here’s the other side of the poster.
Oh and a picture of my RCD trip system in readiness 😉
 

Attachments

  • IMG_0673.jpeg
    IMG_0673.jpeg
    3.2 MB · Views: 22
  • IMG_0674.jpeg
    IMG_0674.jpeg
    1.8 MB · Views: 21
I would fit a new 8 way split load board to the property, that has RCD protection to meet the current electrical installation regulations and detect earth leakage on the external circuit. Also the circuit will have its own correct size MCB on the RCD side of the board. Run a correct sized steel wired armoured cable with water proof glands from the board to a small garage board inside the external building or a small water proof rated board if external. This might have to be fixed at a minimum height from the ground. Route the cable correctly using cable cleats or buried deep enough in the ground with warning electricity tape. Also you it might be wise to fireproof your internal board enclosure like using fire proof board on the inside of the cabinet.
 
I would fit a new 8 way split load board to the property, that has RCD protection to meet the current electrical installation regulations and detect earth leakage on the external circuit. Also the circuit will have its own correct size MCB on the RCD side of the board. Run a correct sized steel wired armoured cable with water proof glands from the board to a small garage board inside the external building or a small water proof rated board if external. This might have to be fixed at a minimum height from the ground. Route the cable correctly using cable cleats or buried deep enough in the ground with warning electricity tape. Also you it might be wise to fireproof your internal board enclosure like using fire proof board on the inside of the cabinet.
I would go for rcbo's
 