HappyHippyDad
Supporter
Bit of an odd question, but as in the title. Can I use 2 x 6mm conductors as my Main bonding to the gas?
I've run out of 10mm, more arriving in a few days, but I could really do with fitting it tomorrow. I know I could just buy some locally, but I just wondered if I could use up my 6mm that I've had for yonks.
Yes, the big [whatever colour this week] book specifically allows for parallel conductors. I'm not at home so can't look it up, but if they same length, samevroute, and no branches should be fine.
Thanks Simon,
I've had a quick scout and I reckon you're pointing to 523.7, conductors in parallel.
Looks like it's fine!
It's just different to the standard, so I wanted to check.
Whilst BS7671 gives guidance on main protective bonding sizes it doesn't suggest how you should achieve these sizes. The use of parallel conductors from what I can see in BS7671 is a different scenario from what you are proposing in that it refers to live conductors.
I don’t see anything wrong with it aside from looking a bit DIY and odd in a domestic setting. I would crimp it both ends if possible so they have a permanent attachment to each other.
A fair few years back I had two submains into a flat, peak and off peak both in 16.0mm² with main protective bonds on a TN-C-S system connected to the peak board. The singular 6.0mm² was undersized so we paralleled the two cpcs together.
Another site a new large school had inadequate main protective bonds in the plant room some distance from the main intake. Solution parallel the existing bonds to a new earth bar in the plant room and upgrade the bonds easily in the plant room only.
I did start typing out that that reg was for live conductors, but then noticed that it also states for PEN conductors. I realise a Main bonding conductor and a PEN conductor have different purposes, but a PEN conductor needs to be sized to handle load current, whereas a bonding conductor only for current under fault conditions (I think). So basically, I'm saying if its a good enough reg for a PEN conductor then it is for a main bonding conductor.
I probably shouldn't have said any of that :rolleyes:
How do you mean 'crimp it both ends so they have a permanent connection to each other? @westward10
I can't picture how you would crimp them together and then join them to the bonding clamp and earth terminal?
oo.. In actual fact, I could just run it all the way out to the gas and then back again in one piece. that would solve the problem at the gas end, but still the earth terminal in the CU?
I'll probably just run a piece of 16mm! I just keep looking at the silly, full reel of 6mm that's been in the shed for years!!
Main protective bonding conductors for TN-C-S are essentially selected to carry current through diverted neutrals should your supply combined neutral/earth fails.
Definitely crimp the ends