HappyHippyDad

~
Arms
Supporter
I've fitted a few EVCP's now, but I have never had to connect an ethernet cable in to one of them as WiFi always works.

My plan is to use a powerline adaptor, is this ok?

Secondly, the EVCP will also need a CT clamp requiring 2 cores. My plan was to use one pair of the cat5e in the EV ultra cable for this as the ethernet connection does not require all 4 pairs. Is this ok?

Thanks everyone.
 
Yes it will be. Re, 2 cores of CAT5 or 6 for the CT, but I don’t know which out of the 8 to use.
I actually think the Ethernet only needs 4… but not entirely sure.

No reason that a powerline won’t work apart from physical distance between socket nearby the hub, route to the CU, and back out to where the EVCP is.

Is Wi-Fi going to be a problem with this one?


While on the subject, I fitted a BG Sync today, (customers choice) … powered up, got it on Wi-Fi. No issues… except, a couple of minutes on, it went into fault mode. Flashing red light - phone technical…
Turns out there is now a silver button on the front that says “press 1 time for rcd test, press 3 x to enter setup”
At no point does it say, “putting on the final decorative cover pushes this button in and holds it in. The charge point will no longer fault”
 
Yes it will be. Re, 2 cores of CAT5 or 6 for the CT, but I don’t know which out of the 8 to use.
I actually think the Ethernet only needs 4… but not entirely sure.

No reason that a powerline won’t work apart from physical distance between socket nearby the hub, route to the CU, and back out to where the EVCP is.

Is Wi-Fi going to be a problem with this one?


While on the subject, I fitted a BG Sync today, (customers choice) … powered up, got it on Wi-Fi. No issues… except, a couple of minutes on, it went into fault mode. Flashing red light - phone technical…
Turns out there is now a silver button on the front that says “press 1 time for rcd test, press 3 x to enter setup”
At no point does it say, “putting on the final decorative cover pushes this button in and holds it in. The charge point will no longer fault”
That sounds soo frustratng!
Many thanks for the advice.
AI seems to imply that using only 2 pairs for the ethernet may not be suitable for some models. I think I'll just pop in some separate SWA cat5e as it's not very expensive.
 
That sounds soo frustratng!
Many thanks for the advice.
AI seems to imply that using only 2 pairs for the ethernet may not be suitable for some models. I think I'll just pop in some separate SWA cat5e as it's not very expensive.
Very frustrating!

Not the first time I’ve needed a tech help desk… I fitted an ICS brand from CEF that had left the factory without being registered. No matter how long I tried setting it up, their cloud didn’t recognise it so wouldn’t allow it to set up. Had to phone up and give them the serial number for them to input it manually.

Now I still need to try and get a point connected to internet in a difficult location as explained on another post
 
Yes it will be. Re, 2 cores of CAT5 or 6 for the CT, but I don’t know which out of the 8 to use.
I actually think the Ethernet only needs 4… but not entirely sure.

No reason that a powerline won’t work apart from physical distance between socket nearby the hub, route to the CU, and back out to where the EVCP is.

Is Wi-Fi going to be a problem with this one?


While on the subject, I fitted a BG Sync today, (customers choice) … powered up, got it on Wi-Fi. No issues… except, a couple of minutes on, it went into fault mode. Flashing red light - phone technical…
Turns out there is now a silver button on the front that says “press 1 time for rcd test, press 3 x to enter setup”
At no point does it say, “putting on the final decorative cover pushes this button in and holds it in. The charge point will no longer fault”

Hi

In the good old days we used 1, 2, 3 and 6 - 4 and 5 were telephone; 7 and 8 spare.
Ref:RJ45 Pinout | Color Code wiring for Network Cable Connector - https://www.cable-tester.com/rj45-pinout/ Think A = American B = British

Now all 8 can be used for Gigabit, but the 4 wires are good for 10/100.
 
Thanks for all the reply's.
I am going to lay a separate cat5e SWA for the ethernet connection, but it would be good to have a definitive answer regarding if just 2 pairs are always ok for a EVCP? I.e. is 100mbps ALWAYS ok for an EVCP, or do some EVCP require all 4 pairs (as AI suggests). I'm not going to do this this time, but it would be good to know for the future.


Thanks.
 
Thanks for all the reply's.
I am going to lay a separate cat5e SWA for the ethernet connection, but it would be good to have a definitive answer regarding if just 2 pairs are always ok for a EVCP? I.e. is 100mbps ALWAYS ok for an EVCP, or do some EVCP require all 4 pairs (as AI suggests). I'm not going to do this this time, but it would be good to know for the future.


Thanks.
If you ask AI the question the other way round "do all EVCPs work on cat5 or cat5e cable", it says "Yes, almost all Electric Vehicle Charge Points (EVCPs) will work over a basic Cat5 (or Cat5e) cable"
It also confirms cat5 or 5e only require 4 conductors.
So take your pick which is 'correct' 🤪
 
Thanks for all the reply's.
I am going to lay a separate cat5e SWA for the ethernet connection, but it would be good to have a definitive answer regarding if just 2 pairs are always ok for a EVCP? I.e. is 100mbps ALWAYS ok for an EVCP, or do some EVCP require all 4 pairs (as AI suggests). I'm not going to do this this time, but it would be good to know for the future.


Thanks.
100Mbps will be fine from a bandwidth perspective although it’s difficult to say it will “always” work with all chargers.
A standard RJ45 port will auto negotiate between 10/100/1000 Mbps, and drop to 10/100 if only 2-pairs are available. That is a valid configuration.
It’s not impossible that a manufacturer might build their charger with a non auto-negotiating RJ45 port which is fixed at 1000Mbps. I’ve seen fixed 1000 ports very occasionally (not on EV chargers), but I’d say it’s unlikely nowadays as auto negotiate 10/100/1000 has been the standard for a while.
 
I thought I would update this.
I have actually been to a different EVCP job. It required both a hard wired ethernet connection and 2 core cable for CT clamp for load balancing.

I fitted 1 x cat5e cable. I use 2 of the pairs for the Ethernet connection, terminals 1,2,3 and 6 and 1 pair for the CT clamp. It all works absolutely fine :)
 