On a site we look after there has been a lot of work done to expand areas. One of the jobs done by contractors is to extend the existing three phase bus bar of an overhead crane and fit an additional crane so there are now two running off the one busbar system. They installed a new supply cable at the far end of the new busbar so the run is now fed from two different supplies, one each end. They did this because the volt drop would have been too much had they just extended the existing busbar with the original feed.

I appreciate it is acceptable to have things fed from two supplies but I began to have concerns when they did it without informing the end users that the busbar now needs to be isolated from both supplies. When I say they did not inform anyone I mean they didn't identify it in their proposal, I honestly think they were not intending to join the two busbars, I don't think they had allowed for the cranes to be able to run the entire length of the busbars and had just thought they would both stick to their own sections. All their proposal identifies is the supply to the new busbar as a seemingly stand alone item. Being an afterthought is reinforced by the lack of signage to identify dual supplies either at the isolators or along the bus bars, everything has been handed over now so should all be in place.

I will be going through the regs but initially, would welcome thoughts:

Whilst the origin of the supplies is derived from the same HV transformer, the routes to the crane supplies are diverse in that part of the extension works was to install a new MCCB panel at the transformer where one switch feeds the old LV panel which in turn feeds the old crane supply, then a new switch serves a new LV panel in a different part of the building which feeds the new crane supply. I don't know the details of difference in volt drop between the two supplies or if there is any equipment biased to either supply that could affect the sine wave. I am pretty sure dual supplies designed to work together need to be from the same source but unsure if this is the transformer or DB.

I will have to check the size of supply cables, protective devices etc as I think these have to be the same but not 100% sure until I consult the regs.

It just seems like I am missing something that I cant put my finger on and would welcome any advice
 
So the original plan was a separate busbar for the new crane but that would have meant it would not have travelled far enough so they have jointed it to the original to make one track?
I'm no expert in these things but I would have thought a single point of isolation was required which would obviously require further paraphernalia such as contactors.
 
Yes, that is correct

So the original plan was a separate busbar for the new crane but that would have meant it would not have travelled far enough so they have jointed it to the original to make one track?
I'm no expert in these things but I would have thought a single point of isolation was required which would obviously require further paraphernalia such as contactors.
Yes, something is off with the installation. The fact that they didnt put any signage up made me think it wasnt planned because it would need to every couple of metres along the busbar which is a real pain to stop production and isolate, takes weeks of planning so they would surely have done it at the time.
 
Exactly but I am more concerned about the voltages and whether anything could affect them being such diverse routes and have yet to check cable sizes and protective devices.
 
On a site we look after there has been a lot of work done to expand areas. One of the jobs done by contractors is to extend the existing three phase bus bar of an overhead crane and fit an additional crane so there are now two running off the one busbar system. They installed a new supply cable at the far end of the new busbar so the run is now fed from two different supplies, one each end. They did this because the volt drop would have been too much had they just extended the existing busbar with the original feed.

I appreciate it is acceptable to have things fed from two supplies but I began to have concerns when they did it without informing the end users that the busbar now needs to be isolated from both supplies. When I say they did not inform anyone I mean they didn't identify it in their proposal, I honestly think they were not intending to join the two busbars, I don't think they had allowed for the cranes to be able to run the entire length of the busbars and had just thought they would both stick to their own sections. All their proposal identifies is the supply to the new busbar as a seemingly stand alone item. Being an afterthought is reinforced by the lack of signage to identify dual supplies either at the isolators or along the bus bars, everything has been handed over now so should all be in place.

I will be going through the regs but initially, would welcome thoughts:

Whilst the origin of the supplies is derived from the same HV transformer, the routes to the crane supplies are diverse in that part of the extension works was to install a new MCCB panel at the transformer where one switch feeds the old LV panel which in turn feeds the old crane supply, then a new switch serves a new LV panel in a different part of the building which feeds the new crane supply. I don't know the details of difference in volt drop between the two supplies or if there is any equipment biased to either supply that could affect the sine wave. I am pretty sure dual supplies designed to work together need to be from the same source but unsure if this is the transformer or DB.

I will have to check the size of supply cables, protective devices etc as I think these have to be the same but not 100% sure until I consult the regs.

It just seems like I am missing something that I cant put my finger on and would welcome any advice
You are right to be concerned, one isolator should isolate the whole crane rail. Electricity kills ,bring this to someone attention who can do something about this.
(maybe cowboys)
 
I'm with Saltburn. Find the Responsible Person for the site and inform them in writing that you believe the installation is unsafe (explain why) and should be isolated until rectified. That covers your backside.

Apart from the safety issue, as you've already considered, it makes circuit protection "complicated". Not only has it increased prospective fault currents in the busbar, pickups, and crane wiring - you also have the possibility of reverse feeding a board, and reducing the current through its upstream protection.
And it's not just the cranes that now have two points of isolation - you have the ability to reverse feed a board that's been isolated for maintenance.

It's out of my experience scope, but if volt drop was a concern then :
The supply should have been uprated. To minimise downtime, it would be possible to pull in a second cable without taking the cranes out of service - and then have a short downtime to terminate it.
It would be reasonable to feed the bus bars at more than one point - provided all supplies come from the same isolator.
 
I'm with Saltburn. Find the Responsible Person for the site and inform them in writing that you believe the installation is unsafe (explain why) and should be isolated until rectified. That covers your backside.

Apart from the safety issue, as you've already considered, it makes circuit protection "complicated". Not only has it increased prospective fault currents in the busbar, pickups, and crane wiring - you also have the possibility of reverse feeding a board, and reducing the current through its upstream protection.
And it's not just the cranes that now have two points of isolation - you have the ability to reverse feed a board that's been isolated for maintenance.

It's out of my experience scope, but if volt drop was a concern then :
The supply should have been uprated. To minimise downtime, it would be possible to pull in a second cable without taking the cranes out of service - and then have a short downtime to terminate it.
It would be reasonable to feed the bus bars at more than one point - provided all supplies come from the same isolator.
Thank You Simon and everyone else that has commented. I also went through the wiring regulations and noted several breaches. Happy to say that the issues have been addressed and rectified. So once again, thanks for everyone's support.
 
How was it rectified?
The existing feed from the old DB has been disconnected and the cables removed. The new isolator that was at the other end of the busbar has been repositioned more centrally of the busbar run. From the new isolator two cables have been run to each end of the busbar, the cable size has been uplifted from 10mm to 16mm to account for volt drop. So now we have a feed to each end but from the same supply and a single point of isolation. The only thing I would have liked to see would have been remote emergency stop buttons but cant have everything.
 