If you do still need to find a suitable termination, pin lugs......

pin-reducer-lugs-250x250.jpg
 
@ E54,

Connect them altogether and improve the overall TT system, using the SWA of your 50mm 4 core cable...

That is what I would have done, for the same reason, but I did not want to contradict the NIC, in case it was for a specific reason they wanted it done this way.
 
Lenny,
You beat me to it a little, though I gave a part no & maker for a 50>35 reducing pin! ;) ;) ;)
 
Sod the NIC, ....They do not make the rules, even though they like to THINK they can!! Ring them and ask for specific reasons Why they want to separate a TT system into 2 separate earthing systems, ....i for one would like to know that one!!!
 
Hi Engineer 54

The load is a 50kw micro generator 70amps/ phase max load, the cable is this size to keep the vault drop within the less than 1% range
There will be four inverters supplied from the sub db.


As for the Nic ,the guy did not give a clear reason about seperating the earths just said do it.
 
Hi Engineer 54

The load is a 50kw micro generator 70amps/ phase max load, the cable is this size to keep the vault drop within the less than 1% range
There will be four inverters supplied from the sub db.


As for the Nic ,the guy did not give a clear reason about seperating the earths just said do it.

That's because there isn't a clear reason!! Different if the source supply was PME, but it isn't so don't try separating the TT system, you'll be defeating the very nature of a TT system...
 
Think what PME stands for exactly...

Protective Multiple Earthing , i know, and yes that is exactly my point!! But by just stating PME on this thread it will confuse the young or inexperienced into thinking along the lines of PME/TNC-S supplies, but that was not really what you (or i) were talking about is it??...lol!!!
 