B
Baker1988
Thanks for all the answer but my boss has just got back to me and said that he is not going to change any thing that it has been that way for years so it is staying that way thanks for all the advice
My point was not that the 10mm would suddenly explode haha , my point was that the cpc of the 10mm twin and earth would be too small So you know that, you have done the equation and it's too small .....fair enough and would need to have its size increased,
for a disconnection time...........We are talking earthing conductors here not R1 + R2, remember the disconnection times are met by both conductors not purely the size of your earth to be met you would need an acceptably low impedence path back to earth, this would increase the fault curent and trip the disconnect in a faster time.......you seemed to have grasped that
The larger an earthing conductor the easier it is for the fault curent to pass through (low resistance) and then the fault current spike increases in direct relation to the impedance.
So the higher the impedance the lower the fault current and the slower the disconnect will go, breaker tripping or fuse blowing,
So the lower the impedance the higher the fault current and the faster the disconnect will go, breaker tripping or fuse blowing.
I know my stuff when it comes to this ......Do you so you cant tell me that leaving the CPC of a peice of 10mm twin and earth as the main earth conductor (TT system or whatever flipping system ) will be more beneficial to a disconnection time than replacing it with a 16mm seperate earth..............Yes I can if I prove it by calculation
Maybe they taught you to use spent dilythiam crystals from the warp drive in college....................not sure what they taught you
They just taught me to use copper cable, dont think any wholesaler I know stocks spent dilythiam crystals or warp drives?
Maybe its a new square D range ?[/QUOTE
Well I'll have to bow to your obvious expertise on this