Discuss Tail size from meter to cu in the Australia area at ElectriciansForums.net

Lloyd apart from the fact that now we have established it is a TT system and they may have to change that switch fuse if the disconnection times can not be met, why are you advocating ripping out things and installing 16mm main earth conductors for a TT earth system?
 
ah ok missed the TT bit :)
thanks

and on the size of he earth (16mm) if he installed it, why would this matter ??

on a TT, your resistance should be under 200 ohms , if he wanted to put in an earth cable that was 125mm that would be ok (apart from look strange )
As long as the earth isnt undersized.

Cant see why replacing the CPC from the cut out to the CU would be a bad thing ?
Yes ensure this meets the disconnection time, but why wouldnt a 16mm earth from the cut out to the CU mean the disconnection time wasnt met?
 
Last edited by a moderator:
Llloyd you could use spent Dilithium Crystals from the Warp Drive of the SS Enterprise if you are so inclined, as long as by Adiabatic equation proves it will carry the fault current.

But what you can't do is advise someone that a T + E sub main on a TT installations need ripping out quick and a 16mm installed, as if that T+E is going to suddenly explode into a roaring inferno, there is no need for a 16mm main earthing conductor on a TT system, and so why advise someone that is the minimum requirements as it isn't
 
My point was not that the 10mm would suddenly explode haha , my point was that the cpc of the 10mm twin and earth would be too small and would need to have its size increased,
for a disconnection time to be met you would need an acceptably low impedence path back to earth, this would increase the fault curent and trip the disconnect in a faster time.
The larger an earthing conductor the easier it is for the fault curent to pass through (low resistance) and then the fault current spike increases in direct relation to the impedance.
So the higher the impedance the lower the fault current and the slower the disconnect will go, breaker tripping or fuse blowing,
So the lower the impedance the higher the fault current and the faster the disconnect will go, breaker tripping or fuse blowing.
I know my stuff when it comes to this so you cant tell me that leaving the CPC of a peice of 10mm twin and earth as the main earth conductor (TT system or whatever flipping system ) will be more beneficial to a disconnection time than replacing it with a 16mm seperate earth.

Maybe they taught you to use spent dilythiam crystals from the warp drive in college

They just taught me to use copper cable, dont think any wholesaler I know stocks spent dilythiam crystals or warp drives?
Maybe its a new square D range ?
 
My point was not that the 10mm would suddenly explode haha , my point was that the cpc of the 10mm twin and earth would be too small So you know that, you have done the equation and it's too small .....fair enough and would need to have its size increased,
for a disconnection time...........We are talking earthing conductors here not R1 + R2, remember the disconnection times are met by both conductors not purely the size of your earth to be met you would need an acceptably low impedence path back to earth, this would increase the fault curent and trip the disconnect in a faster time.......you seemed to have grasped that
The larger an earthing conductor the easier it is for the fault curent to pass through (low resistance) and then the fault current spike increases in direct relation to the impedance.
So the higher the impedance the lower the fault current and the slower the disconnect will go, breaker tripping or fuse blowing,
So the lower the impedance the higher the fault current and the faster the disconnect will go, breaker tripping or fuse blowing.
I know my stuff when it comes to this ......Do you so you cant tell me that leaving the CPC of a peice of 10mm twin and earth as the main earth conductor (TT system or whatever flipping system ) will be more beneficial to a disconnection time than replacing it with a 16mm seperate earth..............Yes I can if I prove it by calculation

Maybe they taught you to use spent dilythiam crystals from the warp drive in college....................not sure what they taught you

They just taught me to use copper cable, dont think any wholesaler I know stocks spent dilythiam crystals or warp drives?
Maybe its a new square D range ?[/QUOTE

Well I'll have to bow to your obvious expertise on this
 

Reply to Tail size from meter to cu in the Australia area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
392
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
886
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
784
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock