For example with a pair of semi-detached houses, it is common to see looping through.
It's very easy to spot... if your service head has two cables, one will be the incomer and the other a loop to next door.
If your service head has only one cable, a quick nosey next door is required to see if theirs has two...
Simon.
Final update.
I sent an email to the customer services with a photo of 1.2 Amps coming down the earth cable with two direct questions. Is this safe? And who is responsible for making it safe.
The next morning I got a phone call from the distributors top trouble shooter who wanted to investigate himself.
He had some difficulty in identifying where the current was coming from, and tried PME’ing the supply 50 meters from the house, but when that did not change anything he came back again the next day with several new ideas.
What they actually did was:
  1. Pull the distributors fuse, then separate their earth cable, from the MET.
  2. With a multimeter, they measured the Amps between their earth and the supply neutral. It measured 1mA.
  3. They then did the same between the MET and the supply neutral. 850mA this time.
  4. Now, they connected the supply earth to the supply neutral, thus giving a very good return path and measured the current with a clamp meter. If there is current coming down their earth, it will flow directly down the neutral. The current was measured with a clamp meter and it measured 0.0mA.
  5. Lastly, they connected the MET to the supply neutral, and this time they found that there was a current of over 3 Amps (The neutral has a reduced impedance compared to the earth so the current would be greater).
    This proves the current is actually coming from outside, through the house system and down the supply earth to the transformer.
Basically, someone in the area has a bad earth connection and is sending current through the ground, and this house has such a good connection to the ground that the current is using the house system as a return path to the transformer, but the voltage drop means the 1.2 amps is at less than one volt.
The Trouble Shooter put another PME connection in at the junction to the main power cable in the road, and was thinking about turning the house into a proper PME system, but eventually he decided the added dangers of PME were not justified in this situation, so the 1.2 Amps measured on the supply earth was actually less than 1 volt and does not pose any danger.
NOTE: The Trouble Shooter is going to retire in June, and has been working on the distribution network for over 50 years. In all that time he has never come across a situation like this. It appears to be a one off.