A

acvc

Not being able to afford a decent clamp meter ....... I was just wondering if electric showers do actually pull their stated load, i.e. the full 10.5/9.5/8.5kW. If they do, is it only as a boost to top up temperate intermittently? Or is it a constant load? I've just been thinking about a few situations I've come across where the MCB is rated lower than the shower load ..... and there hasn't been a problem.

Thanks chaps.
 
Comment removed, could have been viewed as condescending which was not the intention
 
Last edited by a moderator:
Depends on the supply voltage how much current they pull. There is quite a difference in current on a 10kw shower when supplied at the declared supply voltages of 216v-253v. Get a clamp meter you will get a lot of use out of it.
 
Try getting your kit off and getting under a 10kw going at full belt mate, you'll be like a lobster:)
 
I came across a 10.5kW shower on a 40A MCB last week, and the guy had never had a problem with it in years. Just got me thinking.
 
Showers are never on long enough to really overload and trip out a breaker.

Sent from my GT-I9100 using Tapatalk
 
I've just been thinking about a few situations I've come across where the MCB is rated lower than the shower load ..... and there hasn't been a problem.

Thanks chaps.

im a college goer so please forgive me ive got this wrong but refering to the under-rated mcb....

my understanding is that say its a 10kw shower it will pull 43.5A at full chat.
so refering to fig 3A4 in the bgb if 60898 type b mcb was rated at 32A it would take in excess of 10,000 seconds to trip (over 2 and a half hours) does that answer the question or have i got it wrong? will i require my tin hat?

Dave

EDIT: Too slow...simplesimon beat me to it
 
Last edited by a moderator:
Gottahugenoggin. That's great. Thanks for reminding me about that. I'm off to bed now with BGB. It is a dumb post and Trev1 was probably quite right with his original - if removed - post.
 
Gottahugenoggin. That's great. Thanks for reminding me about that. I'm off to bed now with BGB. It is a dumb post and Trev1 was probably quite right with his original - if removed - post.

i like dumb posts!!! then i get a fighting chance to answer :smug:
 
[h=2]What does an electric shower really pull?[/h]well i once heard of a well endowed triton pulling a gorgeous little mira.
 