R
ratboymark
hello
went to see a job today there is a single non switched socket with 20a isolator above work top which is part of the 4mm sockets radial the current oven is wired on a 13a plug, the new oven the customer has bought has no plug or flex and the manufactuers instructions say 16amp supply reqed it would be a massive job to run new cable on 16amp mcb with max demand ect would a 13amp plug be ok or, would there be nuisence triping or would a option be to install a 1 way consumer unit with 16amp mcb in and supply this with the cables which were for the single socket i carnt see how this 2nd option would be a problem whats your thoughts?
many thanks
mark.
are you suggesting that it wont be using 16amp because chances are it wont be on full heat often, and once its up to temp its not using much?
3.5kw i think no regs or on site guide to hand both in van and all previous additions 16 ect sold so carnt check diversity allowances
A 4mm cable is certainly up to the job and as Rauer suggested, with a flex outlet plate it will be fine - also fit a 16A C/B. You are then fully compliant with manufacturer recommendation to cover yourself.
just had a look at diversty it says 100 percent to be calculated, talked to NICEIC on phone he thinks FCU would do the trick because it would never be on full load but, I think the 16 amp MCB sounds like a good plan play it safe thanks for help.
I agree with the 16A MCB, more and more ovens have a self clean feature nowadays as they are getting cheaper to buy. Heats up to 500 degrees celsius for 3 hours to turn the grease into ash. That's gotta be full load.
first 10A....then 30% of whats left.....and if the main cooker switch incorperates a BS1363 outlet.....then just add 5A.....