Final decision think I'm going for to be safe is....

3 days ===> me + 2xlabourers:builder:

1/2 tonne to shift per labourer / day

1 x days for me to make safe / strip down
1.5 x days to install new and test
0.5 x days any unforeseen circumstances
 
Or you could replace them new electric rads, saves half the amount of graft!

Landlord just wants like for like on this one, would make it easier though.

Also I don't have much experience of using electric rads, especially on a job this size - it's big odd shaped area to heat up, old church converted into a mixture of open plan office areas. Cant risk getting it wrong as a good few grands worth of materials.
 
Just make sure the labourers take 2 old bricks down before brining 2 new brick up , why go empty handed ?

Jamie
 
I think caution needs to be exercised with regard to the old heaters as to whether they have any asbestos content that will need specialist removal

The last big removal of storage heaters I did 15 or so years ago the heaters had to be bagged, sealed and removed in one by an asbestos removal contractor about 30 heaters over 2 floors with a combined weight of about 8 tonnes.

Disconnected Friday PM asbestos contractor started at 6PM and finished 9 AM Saturday, we did the install of the new heaters Saturday 8AM till 6PM and Sunday 8AM till 5PM, 4 sparks and 2 labourers.

One last thing will the floor where the new heaters are to be delivered to / stored prior to install carry 3 tonnes or will you have to have some one onsite to distribute the load at delivery time to avoid point loading the floor
 
I think caution needs to be exercised with regard to the old heaters as to whether they have any asbestos content that will need specialist removal

The last big removal of storage heaters I did 15 or so years ago the heaters had to be bagged, sealed and removed in one by an asbestos removal contractor about 30 heaters over 2 floors with a combined weight of about 8 tonnes.

Disconnected Friday PM asbestos contractor started at 6PM and finished 9 AM Saturday, we did the install of the new heaters Saturday 8AM till 6PM and Sunday 8AM till 5PM, 4 sparks and 2 labourers.

One last thing will the floor where the new heaters are to be delivered to / stored prior to install carry 3 tonnes or will you have to have some one onsite to distribute the load at delivery time to avoid point loading the floor

Have checked out the asbestos issue - confirmed serial /model numbers with dimplex - all ok - clear :)
All materials will be distributed evenly when delivered.

Many thanks for your advice Sy
 