Malcolm tells you in post 11 mate. Your lines go into the top end of your MCB, your neutrals go in the neutral bar. Turn off the MCB and line is isolated, the neutral is not as it is connected to all the other neutrals in the installation. Current flows from line through appliance then back down neutral. Obviously some of this is flowing down the neutral where the problem exists thus tripping the RCD.