Discuss TT systems in the UK Electrical Forum area at ElectriciansForums.net
Don't see any evidence of 2391 mate, I'd hope that someone with that would be able to figure out why the RCD is tripping. Maybe I expect too much though
I stand corrected, OP claims a 2391 pass in 2007 on another thread. Now I'm really scared
After reading this thread I decided to take a look at previous posts by the OP and I'm sorry to say that I personally believe this to be a load of BS. I do not have 2392 or 2391 and I would put money on the fact that I could quickly identify and remedy the fault. I'm absolutely shocked to learn that someone with such a qualification (that requires a vast amount of knowledge and in the field experience) could be posting such amateur questions.
UNBELIEVABLE!
UNBELIEVABLE!
Yes, its possible to pass the 2391 without hardly lifting up a tester, screwdriver or even getting your hands dirty!
I was putting off my 2391 for a while until I get a bit more experience, but if the OP has it without understanding the fundamentals of RCD protection then I'm going to enroll tomorrow...
Easy way to demonstrate this. Find a house with upfront rcd, choose a circuit, switch said breaker off at board, open up a switch or socket or FSU on said circuit whatever (make sure the house is nicely loaded up with other stuff like tele, lights, immersion heater etc) - then with a pair of insulated pliers remove the neutral wire from the scoket or switch or fsu and touch it against the metal of the backbox or earth terminal ANNNDDD oh go and get a torch.....
This is standard operating procedure for any spark working on multiple ccts with rcd up front, i.e. trying to work on one circuit without tripping the rcd. LOL
beggers belief dunnit...lol..
found problem when removed one off the spotlight cable had melted together also found what looks like bite marks on cable could have been a mouse
Reply to TT systems in the UK Electrical Forum area at ElectriciansForums.net
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O