not having an rcd does not mean it is potentialy dangerous though , if it was done to 16th ed then surely its just a code 3 IMO
now youre talking about just no rcd's
the issue is no supp bonding AND no rcd's in bathroom = code 2 under 17th ed guidlines
op said no suppleymentary at first so i said code 3
then no rcd came in to it but this is still code 3
same as no rcd on sockets , it does not meet regs but that dont mean its potentially dangerous
no rcd or supp well is that potentially dangerous?
GOOD GRIEF !
its on page 12 of the current ESC coding guide , go and check if you wont believe me.
I would give the sockets for external use from a TT supply with no 30ma RCD protection a code 1
Q4. What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 Ω)
supplementary is not required if main bonding is in place ,rcd is used and ZS values are met
can you say code 2 because code 3's dont get done ??
No I don't say code 2 because code 3 will not get done I say code 2 because it is potentially dangerous.
Undar fault conditions if a person is wet the body resistance is far lower and their is a good chance of serious injury to a person.
Supplementary bonding is required by the regs for this reason Safety!
I understand when and where supplementary bonding is required but IMO even if you have all ccts RCD protected all extraneous parts connected to the MET and bonded and the diconnection times are MET it is still safer to have supp bonding in the bathroom !
Q4. What............
Q4 ?
Hang on , Q4 ???
are you telling me these are exam questions and not a job scenario ?
what happened to " i just did 2 pirs and....." ?
so were doing your homework for you and didnt bother to tell us ?
to$$er.
I was explicitly told during my annual assesment about 5 years ago that all sockets with the possibility of external use shoud be protected by a 30ma RCD and if they are not I should issue a C1, and at what version of the regs did TT supplies not have a 30ma RCD covering socket outlets?
Q4 ?
Hang on , Q4 ???
to$$er.
_______________________________
No that question is taken from the electrical safety council website for commonly asked questions regarding inspections.
Code 2 re the sockets.
So if you are allocating a code 1 what action are you taken to rectify the danger present?
GOOD GRIEF !
it is only code 2 when yhere is no rcd, or no main bonding or disc times are not met
the op never said that ....................