All,

Got a customer who has a 16th edition cu, so 30mA RCD protecting all the socket circuits and whole house is also protected by a 100mA RCD between the meter and the board.

The house has been subject to a number of botches and been fully decorated so ripping it apart could be tricky.

They have very occassional nuisance tripping of the 100mA device - and they think its on a socket circuit, but the 100mA rcd is always the one to trip.

I'm going to go and have a better look but interested to hear from anyone who has experienced anything similar.

Its a TT system and the 100mA isn't technically required as the CU is insulated and the meter/RCD/CU are directly next to each other.

Not ideal but replacing the 100mA RCD with an isolator has crossed my mind!

Tin hat on!

Thanks
 
well as you say its already protected by 30mA rcd so...

i would do insulation resistance on board knocking one ciruuit on at a time or off, then test rcds ....

somethings teeling me an upstream fauult but cant remember what would cause it upstream

and i bet im the last person you wanted to hear from first
 
It can be down to the speed that the RCD's trip. When you test the RCD make a note of the speed that they trip, you may find the the 100mA trip is very fast.....unlike me!!
Phil
 
They "think" the fault is on a socket circuit Murdoch, but if it is on one of the circuits not protected by the 30mA RCD then the 100mA wo​uld be the only one to trip.

Your call but I would leave the up front RCD in place as an added measure of protection (like it's providing now)
 
I reckon discrimination issues between the 30mA device and 100mA device are the reason for the 100mA device being activated first.

I would ditch the 100A.

Nuisance tripping as you well know may be due to a build up of earth leakage over all of the circuits protected by the single RCD. Possibly time to bring the clamp meter out:thumbsup
 
It can be down to the speed that the RCD's trip. When you test the RCD make a note of the speed that they trip, you may find the the 100mA trip is very fast.....unlike me!!
Phil

I remember when testing a dual RCD protected consumer unit that also had a 100mA device upfront the 100mA would trip out the entire installation on x5 tests.

They "think" the fault is on a socket circuit Murdoch, but if it is on one of the circuits not protected by the 30mA RCD then the 100mA wo​uld be the only one to trip.

Good point, this passed me on the first read.

Murdoch, do you know how many circuits are on the unprotected side? :thumbsup
 
I reckon discrimination issues between the 30mA device and 100mA device are the reason for the 100mA device being activated first.

I would ditch the 100A.

Nuisance tripping as you well know may be due to a build up of earth leakage over all of the circuits protected by the single RCD. Possibly time to bring the clamp meter out:thumbsup


Yes, thought about the clamp meter but it would seem that the "dead" of night is when its tripping so as most of the house is "switched off" its unlikely
 
agree ^^^ . IR test and RCD tests are your first call. it's possible that the 30mA is defective so the fault is bypassing it and activating the 100mA. or, as said, the fault might be on a circuit not covered by the 30mA. eliminate appliances as well. good luck with it.
 
They "think" the fault is on a socket circuit Murdoch, but if it is on one of the circuits not protected by the 30mA RCD then the 100mA wo​uld be the only one to trip.

Your call but I would leave the up front RCD in place as an added measure of protection (like it's providing now)

The lighting circuits look bad and as the loft is now a room there is almost nothing to look at.

- - - Updated - - -

agree ^^^ . IR test and RCD tests are your first call. it's possible that the 30mA is defective so the fault is bypassing it and activating the 100mA. or, as said, the fault might be on a circuit not covered by the 30mA. eliminate appliances as well. good luck with it.

Should have said in OP that both RCD's are tripping correctly and as somebody has pointed out the 5x test on the 30mA did trip the 100mA first!
 
more info mrdoch, isit a dual rcd board ???? and if so all circuits protected so the above about unprotected way is out of question, give me clue murdoch , il help you
 
Would it be feasible to move unprotected circuits on to RCBO's and do away with the upfront 100mA:thumbsup

I would be suspecting a fault on the RCD protected circuits (possibly boiler perhaps)? which as a result is taking out the 100mA due to discrimination???

Please keep us posted when you find the fault:thumbsup
 
I'll stand corrected but I'm pretty sure on a tt system you need 100ma cd to protect everything, sound like this is a split load board with 30ma protecting sockets, if he 100ma up front rcd is removed they'll be no rcd protection on the lighs etc which I'm sure it's a no no (being tt)
 
more info mrdoch, isit a dual rcd board ???? and if so all circuits protected so the above about unprotected way is out of question, give me clue murdoch , il help you

socket circuits are covered by 30mA rcd, lighting and cooker are protected by "upfront" 100mA RCD
 