S
sl1210
Hi guys,
I've got a possible job coming up where a client has a portable office in their garden and needs its powered up. Now it is all pre wired with an rcd fusebox inside, 1 socket, 1 light, and 1 13a spur supplying a heater, 20a, 16a, 6a. Basically on the outside of the fuse board there is a plastic isolator where i will need to terminate the armoured too.
Now the problem is the main house is on an old 12 way mem fuseboard without rcd, (no chance of getting an rcbo for the only spare way) Off the main switch they have supplied a 1 way rcd unit which is supplying another garage at the end of the garden on a 40a breaker.
Now ideally i would have loved to have just upgraded the 1 way rcd unit to a 2, but there is no space whatsoever in this cupboard. I might have to somehow make myself some room and henley block the tails so that i can somehow squeeze another 1 way rcd unit in But ain't sure exactly how to do this yet.
Also the run to the cabin is about 13 metres, do you think 10mm 3 core armoured will be enough for that small supply, or shall i go for 16mm??? Also is there anything else i need to take into consideration considering its a special location???
Cheers
10mm swa is fine as its a sub main in swa no need for rcd protection so connect to exsisting consumer unit also portable building should be on a tt system use tncs on supply dont connect incoming earth to office but install earth rod from office consumer unit
the armoured cable doesn't need rcd protection. when i say portable, basically it will be fixed there permanently whilst the tenants are living there.
so are you saying i can't connect the office to the main incoming earth???
thing is i don't think i will be able to get a mem 40a breaker for that old style fuseboard anyway.
I’ve read and re-read the OP, I can’t see any mention of the house supply.
jaydee you may want to rent this (very reasonable rates).
Hi guys,
Cheers
and someone going to live their.... imgrant smuggler, geeeeeeeeeeeees i cud be a detective