Hi,

Trying to get a IR read from Live to Earth yesterday.
IR reading from L - N is fine no problems and getting 115 Mohms at 500v dc from 25 year installation, but when I try to get reading from L - E or N - E my meter will only generate 47V and obviously not produce a reading.
Am I missing something really silly here?

Cheers

David
 
What is the Mohm reading? Sounds like its shorting so it can't generate the voltage
 
The circuit is the upstairs radial with a fault, it is wired into a 16th edition board with no rcd's, the mcb is tripping out, all visual checks look fine, continuity throughout the circuit is fine as well as polarity, I am going to check the outside light today which I think is the cause of the fault.
I just don't understand why I cant get L - E reading.
 
As Tel and I have said if you have a fault N-E and therefore a voltage your meter will detect that voltage and stop the test.

Did you completely disconnect the radial from the CU ie LINE/NEUTRAL/CPC from the CU and test it?
 
any thing left connected? could be capacitance charged up in an appliance.
 
The circuit is the upstairs radial with a fault, it is wired into a 16th edition board with no rcd's, the mcb is tripping out, all visual checks look fine, continuity throughout the circuit is fine as well as polarity, I am going to check the outside light today which I think is the cause of the fault.
I just don't understand why I cant get L - E reading.
outside lamps should be the first thing you look at when doing a visual for faultfinding if connected to the offending circuit....always suspect something that has been exposed to the weather ....and eliminate that first....before moving on.....
 
outside lamps should be the first thing you look at when doing a visual for faultfinding if connected to the offending circuit....always suspect something that has been exposed to the weather ....and eliminate that first....before moving on.....

Next to look at is anything that's "Definitely not been touched" by the occupier.
 
Hi,

All sorted, it was the outside light with a crack in the case, so it was letting in water, and the earth was left unsleaved and had snapped off, so was shorting on the neutral (a right mess inside) .
Now rewired a new unit , water tight with and great IR readings.
Thanks for the tips guys
 