Hi I have been looking at a 1950's flat which is wired in pyro so would this mean RCD protection is not required?
 
It's been a repossession where the person has removed all the light fittings so they want all new face plates alter some points in the kitchen and re fit new lights.
 
No RCD protection required to buried cables which have an earthed sheath which is capable of being used as a cpc....for which pyro qualifies.
Does not mean RCD protection for other purposes is not required though....such as sockets for general use.
 
I thought that piro's do need rcd protection because they are not adequatly protected in the wall like cables in conduit are?????
 
I thought that piro's do need rcd protection because they are not adequatly protected in the wall like cables in conduit are?????

I still believe that MICC cable has the BS classification of BS EN 60702-1 and that is a cable that is identified in regulation 522.6.101 (ii) that does not require RCD protection if installed in a wall less than 50mm
 
Is there a particular reason why you don't want to install RCDs? I mean, the socket circuits and bathroom circuits could do with RCD protection anyway, so if it were me I'd IR test the circuits and bang in RCD protection.
 
Although I know Pyro does not need RCD protection if its buried in the wall, I may cause controversy here, I would still RCD protect the cable as the copper sheath doesn't provide enough protection from penetration of nails or screws.

Anyway, as other posters have said you still need to RCD the bathroom light and general sockets.
 