BobbyNoMates

Evening all

I Have just replaced my 9.5kw electric shower. The new one is also 9.5kw.

My set up is 40a fuse in consumer unit (no RCD), 10mm cable to 45a pull cord, and 10mm from pull cord to shower.

I would like to install an RCD to the shower feed for added protection. I appreciate that it may have to be carried out by a qualified electrician, but would be grateful for any advice, confirmation or slagging off...if that be the case.

I have in mind installing a 63a 30ma RCD unit, between the consumer unit and the pull cord. As far as I know, earth bonding is in place on bathroom pipes (cold water feed pipe to shower earth).

Would a 40a 30ma RCD be more suitable? Also would it be suitable to install the RCD enclosure in the loft? I know it's a bit of a pain for access at test intervals, but would be most convenient for installation purposes.

I do want the installation to be safe...which is why I am considering additional measures, however if it doesn't appear as clear cut as I have mentioned above, then I won't tamper with it.

Any responses will be greatly appreciated. Cheers, Bob
 
Evening all

I Have just replaced my 9.5kw electric shower. The new one is also 9.5kw.

My set up is 40a fuse in consumer unit (no RCD), 10mm cable to 45a pull cord, and 10mm from pull cord to shower.

I would like to install an RCD to the shower feed for added protection. I appreciate that it may have to be carried out by a qualified electrician, but would be grateful for any advice, confirmation or slagging off...if that be the case.

I have in mind installing a 63a 30ma RCD unit, between the consumer unit and the pull cord. As far as I know, earth bonding is in place on bathroom pipes (cold water feed pipe to shower earth).

Would a 40a 30ma RCD be more suitable? Also would it be suitable to install the RCD enclosure in the loft? I know it's a bit of a pain for access at test intervals, but would be most convenient for installation purposes.

I do want the installation to be safe...which is why I am considering additional measures, however if it doesn't appear as clear cut as I have mentioned above, then I won't tamper with it.

Any responses will be greatly appreciated. Cheers, Bob
whats this??
not a requirement....as its like for like replacement...but recommended
no....
sensible...get an electrician in..
 
Thanks, it does state in the manufacturers instructions for the new shower that a 30ma RCD MUST be fitted.
yes what i should have stated is its not a requirement as far as BS7671 is concerned...but manufacturers instructions supercede BS7671 anyway....besides...even if the manufacturers instructions didn`t state that an RCD was required...i`d be fitting one anyway....
 
Not this again noooooooooooooooooooooooooooooo. Yes your right an rcd should be fitted private message spin London and ask him he agrees with me too.

- - - Updated - - -

Oh and glen spark
 
Not this again noooooooooooooooooooooooooooooo. Yes your right an rcd should be fitted private message spin London and ask him he agrees with me too.

- - - Updated - - -

Oh and glen spark

No don't private message, lets have it out here in the open haha
 
You threatened to ban me for this subject MDJ last time. Lol. No 1 agrees with me on this one ever apart from spin obviously.
 
yes what i should have stated is its not a requirement as far as BS7671 is concerned...but manufacturers instructions supercede BS7671 anyway....besides...even if the manufacturers instructions didn`t state that an RCD was required...i`d be fitting one anyway....

Thanks Glennspark..my thoughts exactly. I'm obviously not an electrician, but am a heating engineer and the same rules apply regarding manufactures instructions. Sorry for the wrong terminology for the earthing, maybe supplementary earthing?..... I'm sure you know what I mean anyway!,,..cheers
 
Thanks Glennspark..my thoughts exactly. I'm obviously not an electrician, but am a heating engineer and the same rules apply regarding manufactures instructions. Sorry for the wrong terminology for the earthing, maybe supplementary earthing?..... I'm sure you know what I mean anyway!,,..cheers
main or supplementary bonding Bobby...
 
Ok, the manufacturers' instructions, which BS7671 requires be taken account of, invariably state:
that a fuse should not be used as a CPD,
that DP isolation is required,
that supplementary bonding to all extraneous-conductive-parts in the location is required and
that the circuit should be provided with 30mA RCD protection.
As such either the existing CU will require replacing, or a new CU just for the shower will have to be installed.
Siting the RCD in the loft, is not an option, as it is a requirement that the circuit be provided with RCD protection, not just a bit of the circuit.
Yes the work will require notification.
 
Last edited by a moderator:
Ok, the manufacturers' instructions, which BS7671 requires be taken account of, invariably state:
that a fuse should not be used as a CPD,
that DP isolation is required,
that supplementary bonding to all extraneous-conductive-parts in the location is required and
that the circuit should be provided with 30mA RCD protection.
AS such either the existing CU will require replacing, or a new CU just for the shower will have to be installed.
Siting the RCD in the loft, is not an option, as it is a requirement that the circuit be provided with RCD protection, not just a bit of the circuit.
Yes the work will require notification.

- - - Updated - - -

Ok, the manufacturers' instructions, which BS7671 requires be taken account of, invariably state:
that a fuse should not be used as a CPD,
that DP isolation is required,
that supplementary bonding to all extraneous-conductive-parts in the location is required and
that the circuit should be provided with 30mA RCD protection.
AS such either the existing CU will require replacing, or a new CU just for the shower will have to be installed.
Siting the RCD in the loft, is not an option, as it is a requirement that the circuit be provided with RCD protection, not just a bit of the circuit.
Yes the work will require notification.

so have you conceded? Have I ground you down into submission ? I learnt that move off my mrs she's a pro.
 
main or supplementary bonding Bobby...
Ha ha...you tell me.

isn't main where the earth is connected near to the stop cock where the water comes in the house, and supplementary where the rest of the water pipes are linked together?? However, with how the original shower cold feed pipe was earthed into the earth from the shower it could be main bonding, or am I digging the hole bigger.
 
That's supplementary bonding your main equipotential bonding is your 10mm to your incoming services normally gas and water sometimes a few others, your 4mm earth in the bathroom connected to the shower and possibly the lighting is your supplementary bonding which is now not required if your con unit is rcd protected
 

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Thread statistics

Created
BobbyNoMates,
Last reply from
Engineer54,
Replies
46
Views
5,945
Back
Top