wiganspark

Morning all

Ive been asked to carry out some repairs on a commercial office block which had a test carried out in march last year, the contractor completed a periodic and not an eicr, one of the items picked up was a 4mm 4 core swa carrying 2 circuits(2x16a),2 lives and 2 neutrals and the steel acting as the c.p.c for both circuits, these are on different phases,the contractor has coded this as a 1 but what would it be on eicr ?

thanks
 
On here we like people to have a go of the question before answering.. What was the old title of code 1 on the periodic and what is the title of code on the EICR?

As for code 1.. Do you agree with this ? And why?
 
i understand code 1 was urgent attention and code c1 is immediate action, but i thought it would have been a c2 now, just a general question in case i come acrross something like this in the future
 
What regulation or regulations do you think it is in noncompliant with ??
 
Last edited by a moderator:
thinking about it im not sure if it is a case of non compliance because regulation 543.1.2 mentions common protective conductors, i am unsure that is why i asked on here for assistance
 
ask yourself if you can perceive a real and immediate danger.... code C1., or a potential danger.... code C2.
 
thinking about it im not sure if it is a case of non compliance because regulation 543.1.2 mentions common protective conductors, i am unsure that is why i asked on here for assistance

Well if there's no noncompliance then there should be no code. Any chance of getting in touch with the guy who carried out the report and asking him what was on his mind when he coded it?
 
Well if there's no noncompliance then there should be no code. Any chance of getting in touch with the guy who carried out the report and asking him what was on his mind when he coded it?

client ordering the work has requested more information and asked why a periodic was used at the end of march,but with the niceic cock up wit the release of the certs this is understandable
 
The NICEIC allowed their contractors to continue using the old periodic report format, when the EICR was introduced. (That period has now expired).
As for the for observation made, from the information provided, no code should be applicable. There is nothing prohibiting the use of a 4 core SWA for 2 single phase circuits, providing the tabulated CCC values are adjusted for temperature rise, due to 4 loaded cores. Again a common cpc is compliant.
Perhaps there are other issues with the circuit? More information is required

Cap
 
The NICEIC allowed their contractors to continue using the old periodic report format, when the EICR was introduced. (That period has now expired).
As for the for observation made, from the information provided, no code should be applicable. There is nothing prohibiting the use of a 4 core SWA for 2 single phase circuits, providing the tabulated CCC values are adjusted for temperature rise, due to 4 loaded cores. Again a common cpc is compliant.
Perhaps there are other issues with the circuit? More information is required

Cap

Thanks for that

No the test engineer just highlighted it as a code 1 then just put n/a on all other aspects of the circuit detail, ie n/a for r1/r2,zs etc
 
The NICEIC allowed their contractors to continue using the old periodic report format, when the EICR was introduced. (That period has now expired).
As for the for observation made, from the information provided, no code should be applicable. There is nothing prohibiting the use of a 4 core SWA for 2 single phase circuits, providing the tabulated CCC values are adjusted for temperature rise, due to 4 loaded cores. Again a common cpc is compliant.
Perhaps there are other issues with the circuit? More information is required

Cap

Agreed, and can't really see there being a problem with 4mm csa and In of 16A
 
4 Core MICC cable was commonly used for ring circuits in it's day, though the cores wasn't on separate phases, but basically the same situation. Not something i would personally do without giving some thought, but perfectly compliant as far as the common CPC issue!! No different, to say running these 2 circuits in a conduit containment system, providing all parameters are compliant!!
 
Did this regular on sales floor refridge cases. Loads were alternate when defrost kicked in and just blower fans normally.

Was always derived from a double pole mcb in a Merlin or Sq D board, 2 phases/ circuits per cable.

2 earths off the banjo for the correct slots in the db earth bar.