What happens if the destructions are only in german or whatever? Then what do we do lol...guess? :38:
 
I always check the wattage on heaters and fuse down accordingly, but thats because theres always a FCU handy...never thought about it for fans, it involves bloody extra-work thats why kingeri haha.
 
switchfuses-2.jpgstruggling with3 amp fuses though
 
The rcd is going to save us all though , if it doesn't the regs are a waste of time (.Cos the supply cable still has the CPC attached doesn't it)

Vortex for one don't call for a 3 amp spur. Or they didn't before this.

Meant Vortice.
 
Last edited by a moderator:
When will you all understand that BS fuses within Plug-tops and FCU's are there to protect the leads and cords supplying appliances/equipments, they are not for protection purposes of the appliances etc themselves!! Any protection afforded to to such items would be purely coincidental. BS 1362 fuses are not and never have been designed to protect appliances/equipment, in many cases the protection curve is far too coarse to afford any meaningful protection!!

So a bit like this Poll, Meaningless!! lol!!
 
When will you all understand that BS fuses within Plug-tops and FCU's are there to protect the leads and cords supplying appliances/equipments, they are not for protection purposes of the appliances etc themselves!! Any protection afforded to to such items would be purely coincidental. BS 1362 fuses are not and never have been designed to protect appliances/equipment, in many cases the protection curve is far too coarse to afford any meaningful protection!!

So a bit like this Poll, Meaningless!! lol!!

Not taking an issue with you E but if the manufacturers instructions say fuse down to 3A how would you deal with it?
 
Not taking an issue with you E but if the manufacturers instructions say fuse down to 3A how would you deal with it?


They can state what they like, it would only apply to the connecting cord or lead, NOT the fan itself. If that required 3A protection, then it's down to the manufacturer to provide that protection themselves, not the circuit installer!!...
 
They can state what they like, it would only apply to the connecting cord or lead, NOT the fan itself. If that required 3A protection, then it's down to the manufacturer to provide that protection themselves, not the circuit installer!!...

So the numpty Scheme assessor comes along and gives you a black mark as the manufacturers instructions haven't been followed....
 