Has anyone got any ideas why a lighting circuit would randomly trip the mcb?

The maximum Zs tested was 1.07 ohms.

Its only ever happened (3 or 4 times) when the 2 wall lights in the front room are switched on. They both have energy saving light bulbs and none of them ever blow.

It doesn't trip the rcd, just the mcb.

Thanks
 
Hi all

Has anyone got any ideas why a lighting circuit would randomly trip the mcb?

Yes I have several Ideas, it is very straight forward identifying the problem without doubt, however to be helpful murdock actually gave you the solution, happy testing :biggrin5:
 
so the problem is the 2 wall lights when switched and yet the IR is fine? hmm, must be the wall lights or one of them then??????
 
Do energy saving lamps ever cause nuisance tripping?

I did a full insulation resistance test on the individual circuit and measured >299 on L - N, L - E and N - E.

The only other possibility is that the tv amp has been tapped off the lighting circuit but that has a perminant feed and not being switched.
 
An MCB will only trip if its dead short or overload. You have ruled out dead short with IR result (Assuming there correct) so then its over load. Whats the total load ?
 
Random thought given the weather, I don't suppose we have any outside light on this circuit, condensation build up, then dries out and fault disappears .