r u for real? change the sockets to spurs and voltage drop does not come into it

go and read the regs for voltage drop

GN3 2.7.19 verification of voltage drop

ie: change to spurs and no one could come along and plug something else in

is that in the regs?


Jesus, please don't tell me you're actually pretending to be an electrician for money.
 
GN3 2.7.19 verification of voltage drop

I can't interpret the guidance notes nor the refered BS7671 regs (612.14 or 525), make reference changing sockets to spurs, means you can negate vd. Perhaps you can clarify for us to learn. PS Guidance Note 3 (No1 2011) has moved Verification of voltage drop to 2.7.20. This refers to motor starting periods of high inrush currents &/or manufacturer reasonable recommendation.
 
I install 240v transformers at columns which give me 24v for camera.
transformer has operating voltage between 220 and 240. My cams have min op voltage of 18v.
 