The current carrying capacity of your cable should be greater than the I2 value of your circuit breaker (unless you are supplying a machine with heavy starting current) so why the hostility?
What does 433.1.1(III) say.... then read you opening post.
 
stand back boys , i got it covered....

Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.

tell me again why fitting lower rated mcb's saves the planet ? it doesnt actually reduce power consumption in any way ???????
 
Hi All,
If you match the I2 value of BS EN circuit breakers to the current carrying capacity of T&E cable a 4.0mm final circuit (referred to generally as a radial) should be protected by a 20amp circuit breaker.
The same theory also means that a 2.5mm T&E ring final circuit should actually protected by a 25amp BS EN circuit breaker!
2.5mm final circuits (referred to as radial) should be protected by 16amp BS EN breakers.
1.5mm - 10amp BS EN circuit breakers.
1.0mm - 6amp BS EN circuit breakers.

Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.

Second it will provide work for unemployed electricians.

What a load of total nonsense. If you can't post anything sensible then don't bother posting. I don't appreciate people coming on here trolling and trying to get a reaction from the forum members. Any more and you will be banned (AGAIN)
 
The current carrying capacity of 4.0mm T&E is 36amps (from memory) and the I2 value of a 32amp BS EN breaker is about 46amps (from memory), so what happens when a fault occurs or when the circuit is overloaded at 36 - 45amps?
The cable is overloaded and damaged prematurely!
Damaged/overheated cable has a reduced CSA making it easier to overload in the future, resulting in more damage and eventually fire.
Heating cable in itself is a waste of energy!
 
Banning somebody for making valid and sensible suggestions/comments is just silly!
Banning people for being rude and offensive would make more sense and lets face it, so far many of you have repeatedly been rude and offensive.
 
The current carrying capacity of 4.0mm T&E is 36amps (from memory) and the I2 value of a 32amp BS EN breaker is about 46amps (from memory), so what happens when a fault occurs or when the circuit is overloaded at 36 - 45amps?
The cable is overloaded and damaged prematurely!
Damaged/overheated cable has a reduced CSA making it easier to overload in the future, resulting in more damage and eventually fire.
Heating cable in itself is a waste of energy!

Which is why we design circuits to avoid small overloads over an extended time period. It's a bit late to try and justify the total ludicrous carp you opened with.
 