LlandrilloSpark
Andy that cracked me up
What does 433.1.1(III) say.... then read you opening post.The current carrying capacity of your cable should be greater than the I2 value of your circuit breaker (unless you are supplying a machine with heavy starting current) so why the hostility?
Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.
Hi All,
If you match the I2 value of BS EN circuit breakers to the current carrying capacity of T&E cable a 4.0mm final circuit (referred to generally as a radial) should be protected by a 20amp circuit breaker.
The same theory also means that a 2.5mm T&E ring final circuit should actually protected by a 25amp BS EN circuit breaker!
2.5mm final circuits (referred to as radial) should be protected by 16amp BS EN breakers.
1.5mm - 10amp BS EN circuit breakers.
1.0mm - 6amp BS EN circuit breakers.
Now it makes perfect sense to adopt this thinking for two reasons:
First it is more efficient therefore saving the planet and will prevent overloading of cabling therefore reducing the risk of fires.
Second it will provide work for unemployed electricians.
The current carrying capacity of 4.0mm T&E is 36amps (from memory) and the I2 value of a 32amp BS EN breaker is about 46amps (from memory), so what happens when a fault occurs or when the circuit is overloaded at 36 - 45amps?
The cable is overloaded and damaged prematurely!
Damaged/overheated cable has a reduced CSA making it easier to overload in the future, resulting in more damage and eventually fire.
Heating cable in itself is a waste of energy!