Hi can some one please inform me what the maximum single phase supply I can get into a house. I'm currently working on a large property that has been converted into 4 flats. (Converted in th 50s) there is only 1 large Lucy fuse.
 
Depends on the loading, and also the supply cable size, you need to calculate the total demand for each flat then go from there. You might have to contact to dno and get the supply upgraded if needed
 
Are you intending to get the DNO to upgrade the supply to a larger one or are you going to just split the existing supply between the residences? If you're getting a larger supply I would go with 3-phase.
 
Thanks for responding

yes there's a 4 way 60 amp panel board with fused neutrals at the moment.. With a large Lucy fuse carrier and I'm guessing it a 100 amp but looks bigger ?? With 25mm tails
 
Fused neutrals? Is this a domestic installation? Do you have a photo handy of the existing setup?
 
photo (4).jpgphoto (4).jpg
 
100 amp is the largest single phase domestic supply I would suggest upgrading to a 3 phase and utilising the phases accordingly. This can be pricey though for the upgrade
 
well it started with a low earth reading in the flat then i discovered this and that there want a earth in site.
 
I'm a bit confused, I thought there was a problem with the size of the DNO supply being insufficient. How did you get from a poor earth impedance test result to the maximum size of single phase supply that might be available.

What was your earth impedance reading? What type of earthing arrangement is there at the moment? Is it TT, TNCS....do you have any photos of the incoming cable?
 
Hi can some one please inform me what the maximum single phase supply I can get into a house. I'm currently working on a large property that has been converted into 4 flats. (Converted in th 50s) there is only 1 large Lucy fuse.

If you are a competent electrician you would know this
 
2.24
And theres no sign of any earths at the main incomer I'm guessing that it was getting an earth from a service. In the flat there is just a metal conduit with 16 mm tails and the earth in the flat is strapped around it TNS.
 
If that's a 4 way 60A Ryefield panel, where is the timer, socket outlet and the other bits being fed from?? First call is to the DNO, to find out if PME is available. If you say this set-up has been in place since the 50's, there doesn't seem to be a problem with the size of supply!! So what about the bonding of the incoming water and gas services,....none i take it??

What is needed, is a replacement Ryefield panel, can't really be having fused neutrals in this day and age.. lol!!

When all said and done, the size of the incoming supply is the least of your problems!!! By the way that DNO cable looks like a relatively new concentric cable, rather than a PILC able. So that definitely wasn't there in the 50's... lol!!
 