I understand where your initial argument/debate is generated from but reg 433.1 actually states the design of the circuit is unlikely to have a small overload for a long period... if you are in the senerio you are debating about then the circuit has been designed wrong and you are in breach of the regs anyway... the senerio you are using as you defense should not occur for a long duration, short duration can be acceptable and is common on some old ring mains and even if you had a cable for example rated at 36 amp pulling say 45amps its been allowed for by the research into the structure and tolerances of the cables we use.

Ive seen over my many yrs cables drawing 15+ amps past their rating for yrs before ive come across them and other than been discoloured slightly they are still holding integrity (well just) but these conditions were caused because copper wire had been fitted in place of fuse wire thus overload wasn't detected...yes they ran quite warm but didn't fall apart or combust.
 
Last edited by a moderator:
So is the stumbling block the so called fusing factors?? but these are also tripping factors David and are as i'm sure you know written in the BS EN 60898 standards for circuit breakers.......not that I've read them
 
small overload for a long period......now what is a long period? greater than the conventional time of 1 hour but how long? 2 hours? a week? a month? a year? 5 years? 10 years? 20 years? wheres my wine......
 
Well I've read it all, every comment, every post and I can now say that I have completely lost the will to live. I can't add to this thread because it's all been said. The original post is utter nonsense and no matter how much the op argues the point it will remain utter nonsense. Think I'll come back next week and see what's going on. Until then, I'm out.
 
Just think, of all those ring circuits installed over the last 70+ years, (not to mention the Radials). ......All it seems were incorrectly protected, from the 30A 3036, 30A 1361, 30A Type 1+2 MCB's, and now the 32A Type B MCB's!! ...What a Revelation!! lol!!
 
I dont think its nonsense, in fact I quite like posts like this....something to make you think, to have a look in certain books, debate is good, opinion is good, herd mentality is bad
 
Perhaps I dont actually exist, oh well........:sick:

Loving that avatar of Catweazle mate. One of his favourite words used to be electrickery. :D
Anyway, pass the popcorn will you. Loads of people will be finishing work soon and this thread will take on a whole new dimension. I might even join in with some electroquadrangulation if I get really bored with laughing my t!ts off…lol
 
rubbish is still rubbish though, and the reason it is - is because in practice the cable does not melt with the B7671 regs breaker size, its as simple as that.
Between all the 50 pluses on here i think we would have spotted it by now.
 
rubbish is still rubbish though, and the reason it is - is because in practice the cable does not melt with the B7671 regs breaker size, its as simple as that.
Between all the 50 pluses on here i think we would have spotted it by now.

Fair point, but sometimes it takes a little bit of so called "rubbish" to make you think, go over some stuff and refresh and you never know pick something up on the way who knows.........but to just keep taking the pee and saying it's rubbish or he's mad without any discussion imo is a little short sighted..............
 
I dont think its nonsense, in fact I quite like posts like this....something to make you think, to have a look in certain books, debate is good, opinion is good, herd mentality is bad

So what are you going to do now and in the future then, only wire 16A radials socket circuits??

The law of averages, tend to favour herds being on the right side of the line, while the maverick's are on the other!! lol!!
 
So what are you going to do now and in the future then, only wire 16A radials socket circuits??

The law of averages, tend to favour herds being on the right side of the line, while the maverick's are on the other!! lol!!

Tell that to Nikola Tesla and George Ohm
 
Mr Cockburn

DonQuixote_zps503ab97d.jpg
 