Morning guys
Currently on a 4 bed rewire,on outside wall I have 2 cavity boxes one housing the gas meter and one housing the head and meter, the old consumer unit was on wall directly behind this box but is now being moved
My question is that on this TNS supply can I bond the gas straight to the MET as it is right next door and then bond the water in the new board or have both got to be at either the MET or at the new consumer unit
Thanks
 
prefer to see both bonds (gas and water) terminated at MET.
 
prefer to see both bonds (gas and water) terminated at MET.
I prefer to see it and do it that way too but i can't see a problem in doing it the op's way either, depends how far the extra run is, if its only a few meters it would be better to have them both at the MET
 
if it's a problem routing one of the bonding cables, then it's OK, agreed. as long as it's mentioned on the cert.
 
if it's a problem routing one of the bonding cables, then it's OK, agreed. as long as it's mentioned on the cert.
Indeed and you know how we all love labelling everything, a label could be made and slapped on the cu too:D
 
i always make sure tha 1 of the labels covers 1 of the cover screws on the CU. then if i have to call back anytime, i'll know if some muppet has been messing in there.
 
Both bonding points should be within the property footprint, ie ..Internal!! So where is your MET actually going to be, in the cavity box, the old CU position, or at the new CU location. The problem comes when you want to conduct a Ze test at the consumer unit, you will need to disconnect the upstream gas bond first!!
 