P
Piratepete
Hi Guys
I don't normally do 3 phase so just need to confirm this.
Local church has a 100 Amp TNCS 3 phase supply. All electric heating spread across phases.
I have to put a supply to a new extension also with electric heating, water heaters, hand driers etc. I'm proposing running the heating off one phase and the rest off another.
I'm proposing a 63 Amp 3ph Switch fuse at the meter end supplying 2 CUs in the extension via a 22metre long surface mounted 4 core 10mm SWA XPLE cable using one core as earth (I prefer this to using SWA as earth)
Is this OK? In particular cable and earth size.?
Pete
How are you going to run 3Φ+N and an earth in a 4C cable? Use the 4 cores for the 3Φ+N and the armours as earth.
Is there is any extraneous services/metalwork etc, in this new extension?? If so, he won't be able to use a 4 core SWA on it's own, it'll either have to be a 5 core, or the 4 core with a separate bonding conductor!! lol!!
Hi Guys
Pete
How are your loads at the origin going to be balanced? I would recommend you run in a three phase sub main to a three phase dist board and do the thing properly.
well if its say tn-c-s if he has more than 10mm armour can he not just add to this for bonding??? why not?
isit because is being used as main earthing conductor
- - - Updated - - -
<< its hard being experienced confident spark..
- - - Updated - - -
No you can't, SWA and copper conductors have different resitivity K factors, so you can't just add together and hope for the best!! It doesn't work like that!! lol!!
but surely of 16mm swa the armour i think = 30mm copper ... so is fine and danty...
Copper is something like 8 times that of SWA, so think in terms of around a 70mm SWA being required for a 10mm copper equivalent!! lol!! Off the top of my head that, but it gives you an idea of WHY!! lol!!
Why cant he use the core for the earthing conductor as a combined earthing and bonding conductor. If it is 10mm2 surely that is big enough. If the supply neutral at the head is 35 or less than the 10mm is big enough for the bonds!
images
Hi Guys
Thanks for all your interest. First, cost is a factor on this job (isn't it always!) Client thought he could just have a 1ph supply and a domestic CU. lol. Requirements have changed today (again)!
Yep, you're right! You've clarified my muddled thinking! Best is a 3ph board, 4 core SWA using the armour as earth. I can just about balance demand across all phases. Max 35 amps/ph so may even drop to 6sqmm ( with 40 Amp fuses in the switchfuse) after checking volt drop calc. Whether 10sqmm or 6sqmm I think I'm correct in saying that the Cu equivalent csa of the armour on both sizes is 13.5 sqmm and 11.5 sqmm respectively so no seperate earth required.
Re bonding - none required at the mo. - no extraneous services/steel (water only in plastic).
I assume that if bonding is required, I have to take a seperate 10sqmm conductor all the way back to main earth terminal in the meter cupboard?
Cheers
Pete
Based on what you have said in your last post, I personally would opt for 10mm sq cable. The type of loads you have specified you are supplying seem quite juicy to me. Another thing to consider is future add ons? I know this is an extension but for the sake of 22m of 10mm you give the client better options in the future. Who knows they might turn around and say, the heating is insufficient lets slap a couple more in?
re bonding it needs to go back to the main earth terminal as the csa of the armour your running would be insufficiently sized.
Piratepete,
Engineer54,