So you can use the armour OF SWA IN DIS CIRCUIT AS bonding conductor if it is sized correctly, is there a table for this or can i see where this is and work it out for myself.. Maybe with help from yourself with my buts and whats, y
I have my own table, cant remeber where i got it from but it shows you the cross sectional areas of swa required as an earthing conductor along with what size is suitable and what isnt.
I'm getting confused here. If I was main bonding services in the extension I would be running a separate earth conductor from the MET............end of. Is it because the supply is to a DB and not a load that he is allowed to use the armour as a bonding conductor??
yes i would do it that way too, but ive seen the armour used as a bonding conductor when the csa is sufficient.
I'm relieved it was a DB. But like we both said, separate Earth for main bonding.............I wouldn't do it any differently regardless of what I've seen.
yeah i agree. but you cant legislate for the way other people do things sometimes, especially when they dont do it the way you would do it and your trying to find a fault. :)
So for my 16mm 5c swa as im not using swa as cpc i could use it as bonding conductor as it would be equivelent to 31mm copper
meaning i could run bonding to this board instead of back to met at service fuse?
Could i use armour as cpc and bonding conductor in this case