G
gap30
Care to explain please
Really?
Care to explain please
FFS!!.....do you really think the DNO would fit a 951 clamp???.....it would have been fitted by a sparks and not the DNO.
I work in a Northern Powergrid Area, we were advised on our last scheme assessment to note down BS951 clamps on EICRs and to contact NPG of situation to rectify, got a letter in the post to the office saying NPG no longer fit BS951 clamps and do not replace BS951 clamps if there is a sound electrical connection.
The letter seemed to imply they did fit them once upon a time.
They did and still known to fit BS951 clamps!! Whether or not that's been or is official policy, i don't know. Actually seen them fit one to my sister incoming cable, when they came to fit an up-rated service fuse and meter!! So it's sure been the case and has been documented here in various threads too!!...There are many TNS lead connections in my region and I've only come across a few 951's,and of those it was obvious they were not fitted by the DNO Personally i wouldn't dream of fitting a 951 clamp to an old PILC cable, but i'd have no hesitation fitting a constant spring earth clamp!!
As for the NICEIC, well wonders never cease!! I wonder how they intend to enforce any of these wild statements they come out with, on what's now becoming a regular basis!! lol!!Like most of the others on here you have missed the point. You state above you would not dream of a 951 clamp on a lead sheath and yet jump on the NIC for advising their members to code them when they find it on an EICR....bit of a contradiction there I'd say.
FFS!!.....do you really think the DNO would fit a 951 clamp???.....it would have been fitted by a sparks and not the DNO.
I neither know nor care. The NIC are yet again making waves for no good reason as it's a very simple matter. If the earth reading is acceptable then there is no need to code it at all, at the absolute most a brief mention in the notes. If it is outside of tolereance then the DNO should be notified and action taken based on what if anything they would like you to do with their equipment.
So are you of the opinion that a 16mm earth wire stripped back and bound to the lead sheath with string would not be coded as long as the Ze reading was acceptable?
All the NIC are stating is that a 951 clamp is not suitable for a connection to a lead sheath and should be coded.....
Hey guy what's the name of the clamp the dno use has it got a name like the BS951 ???
Originally Posted by Engineer54![]()
![]()
They did and still known to fit BS951 clamps!! Whether or not that's been or is official policy, i don't know. Actually seen them fit one to my sister incoming cable, when they came to fit an up-rated service fuse and meter!! So it's sure been the case and has been documented here in various threads too!!...There are many TNS lead connections in my region and I've only come across a few 951's,and of those it was obvious they were not fitted by the DNO Personally i wouldn't dream of fitting a 951 clamp to an old PILC cable, but i'd have no hesitation fitting a constant spring earth clamp!!
As for the NICEIC, well wonders never cease!! I wonder how they intend to enforce any of these wild statements they come out with, on what's now becoming a regular basis!! lol!!Like most of the others on here you have missed the point. You state above you would not dream of a 951 clamp on a lead sheath and yet jump on the NIC for advising their members to code them when they find it on an EICR....bit of a contradiction there I'd say.
he told me that the NICEIC are now saying any TN-S with no soldered connection (earth clamp on metal sheath etc) should be made into a TT
the NICEIC are soon going to insist on this.
It’s going take a lot of pressure to damage a PILC with a BS951 clamp. With regard to clamps becoming loose over time, the same problem would occur on water pipes especially hot water.
Hepworth clamps need an application tool for correct tension. Constant force springs applied correctly with a bed of copper braid around the lead provide an excellent and flexible connection.
At the end of all this, it is not you’re responsibility! Nor is it the responsibility of the NIC to give out advice on DNO matters. You’re only recourse is to contact the DNO.
strip a bit of 6mm single. wrap around lead sheath then get a plumber to solder on with blowtorch. stand well back.