I have been asked to price to add some more sockets and lights to a garage plus a few out side sockets.
now the garage already had a supply from the house via SWA cabling which just feeds a socket and the lights via a fused switched spur.
now the consumer unit in the house is an old "Ashley & Rock" with Supasafe MCB's. with blue writing if that helps the whole lot is protected with one main RCD.

Now for my question.
I know that I can fit just a 2 way unit but I was thinking that with more sockets and some of them outside it would be better to fit an RCD in the garage.
but I need this to trip before the house RCD trips so any suggestions would be great.

Thanks for all suggestions
 
Hi, Im sure if you put a standard 30mA 40ms rcd in the garage consumer unit then this will switch before the rcd in main house consumer unit. So hence the main power to the whole house will be unaffected.
 
It's called rcd discrimination. You can change the main house rcd to a time delayed 100ms. Or of you slam an earth rod in the ground off the garage earth terminal then this will prob trip it off quicker if the ground isn't really dry!!
 
Evening everyone

I have been asked to price to add some more sockets and lights to a garage plus a few out side sockets.
now the garage already had a supply from the house via SWA cabling which just feeds a socket and the lights via a fused switched spur.
now the consumer unit in the house is an old "Ashley & Rock" with Supasafe MCB's. with blue writing if that helps the whole lot is protected with one main RCD.

Now for my question.
I know that I can fit just a 2 way unit but I was thinking that with more sockets and some of them outside it would be better to fit an RCD in the garage.
but I need this to trip before the house RCD trips so any suggestions would be great.

Thanks for all suggestions
Whats wrong with leaving it as it is?
 
if your on a tt system 100ma td rcd protecting sub main to garage then 30ma rcd in garage if tncs the swa feeding the garage does not require rcd protection just protect it by mcb in house and fit 30ma rcd in garage
 
What you talking about Murdoch!! He wants rcd protection in the garage simply so if a fault occurs in the garage then it won't trip the rcd in the house! Obviously the feed to the garage is swa and this obviously requires protection from the main ccu mcb and rcd. All the circuits in the garage will be protected by this also but if you want garage to trip first then you will require discrimination. As I have said above.
 
Hi, Im sure if you put a standard 30mA 40ms rcd in the garage consumer unit then this will switch before the rcd in main house consumer unit. So hence the main power to the whole house will be unaffected.

You clearly have no understanding of discrimination, or how to overcome them!!

Contary to your pridiction, it is far more likely that the house and the garage will both trip, and more probable that the house RCD will trip before the garage, if the house RCD is also looking at several other circuits!! So putting it bluntly, you are WRONG!!
 
It's called rcd discrimination. You can change the main house rcd to a time delayed 100ms. Or of you slam an earth rod in the ground off the garage earth terminal then this will prob trip it off quicker if the ground isn't really dry!!

No you can't, Your then adding an unwanted delay to the additional RCD protection to the house circuits. How an earth rod is going to get anything to trip quicker, is beyond my understanding!! ...lol!!
 
If you take cumulative leakage in to account the house would most likely go first.

Exactly!! lol!! Plus the fact that a typical fault would be far in excess of 100 mA, so they would both trip in that scenario too!!
 
What you talking about Murdoch!! He wants rcd protection in the garage simply so if a fault occurs in the garage then it won't trip the rcd in the house! Obviously the feed to the garage is swa and this obviously requires protection from the main ccu mcb and rcd. All the circuits in the garage will be protected by this also but if you want garage to trip first then you will require discrimination. As I have said above.


Wrong. The op mentions a RCD but what value is it? You can't go slamming in a 30mA RCD in the garage and a earth spike without considering the impact.

The OP needs to more clearly define what the situation is then maybe and only then, can we give constructive comments!
 
What you talking about Murdoch!!
He wants rcd protection in the garage simply so if a fault occurs in the garage then it won't trip the rcd in the house! Obviously the feed to the garage is swa and this obviously requires protection from the main ccu mcb and rcd. All the circuits in the garage will be protected by this also but if you want garage to trip first then you will require discrimination. As I have said above.


hahahahaha. this sounds like b.a. doing an impression of arnold.

 
why would SWA require RCD protection?
 
whats the solution then? is worth having a RCD on the workshop and not trip the house when some machine goes wrong.
Time delayed rcd/rcbo in the consumer unit (just for outside circuit) to protect the cable run, then normal 30ms in the garage maybe?
 