lofty84
well if 1.5 is 17 amps
17/1.5 = 11.33 something
11.33 x 2.5= 28 something
11.33 + 28 = 39.33 something
17/1.5 = 11.33 something
11.33 x 2.5= 28 something
11.33 + 28 = 39.33 something
well if 1.5 is 17 amps
17/1.5 = 11.33 something
11.33 x 2.5= 28 something
11.33 + 28 = 39.33 something Since when did we have 3.5mm2 cable?
the cable is not directly going into the MCB thats probably a silly answer.
no it would not as it would obviously get to hot deteriorate and catch fire.
thinking about it now a 2.5 mm cable can take 28 amps which would do the same however as it is a ring the 32A is split so there is only 16A on each leg therefore the 2.5mm cable which can only carry 28 amps or so is fine. in theory then you could do a ring in 1.5 although as it can only carry 17 amps and the breaker gives 16 amps per leg this is pushing it a bit.
see its in there