my new oven needs hardwiring but all there is in oven housing is a cooker outlet which 6kw hob is wired to and a single socket wired off this for plug in oven am i right in changing the front of socket to a DOUBLE POLE SWITCHED
FUSE SPUR OUTLET cu as 32a mcb also 45amp ccu on wall in kitchen
 
what's the rating of the oven?
 
should be OK on a 13A FCU then. 1 point. the rating of the cooker isolator is irrelevant. the 45A is just it's max. load. make sure you use a decent FCU , not cheapo rubbish.
 