I went to a job yesterday, the house was quite old and found some interesting wire I'd never seen before. It's part copper inside, very alloy like on the outside and it's stranded.
wiring.jpg
Does anyone know what this is?
 
Sounds like lead sheathed cable. If it is its best not to connect to it & better to remove it and rewire the circuit. If the client doesnt like the sound of that I would walk away from the job.
 
tinned copper by the looks of it. what's the insulation? is it T/E or singles?
 
who says it's crap? if you answer my previous post.......
 
posted before reading that. OK. ot's pvc/pvc. IR test it if it tests OK, what's the problem? what size is it closest to? can't tell from the pic.
 
It'll be 7/029, 7/036 or 7/044, (2.5, 4.0 or 6.0) tinned, nothing wrong with it if the I.R is O.K

Life was easier when all cables were multistrand.
 
I can't see it can be anything else than tinned copper conductors!! Cut it with a pair of snips and it can look like more tinning than copper. I take it this is imperial sized cable, and as such has a higher CCC than the what really is ''Crap'' solid core metric equivalent!! lol!!
 
tell me about it. when you need a conduit bender to bend 2.5mm solid cable when it's cold.
 