I think that you are correct , yes.

The timer is designed so that with live to 3 and neutral to 4 the timer function will operate.

If the link described in the instructions is not present then there will be no voltage on 1 or 2 at any time.
However there is an internal switch that joins 1 to 2 when the timer is on, this is electrically independent of 3 and 4.

If the link between 2 and 3 is in place then there would be 230V at 2 all the time and this would be connected to 1 when the timer is on.
 
I think that you are correct , yes.

The timer is designed so that with live to 3 and neutral to 4 the timer function will operate.

If the link described in the instructions is not present then there will be no voltage on 1 or 2 at any time.
However there is an internal switch that joins 1 to 2 when the timer is on, this is electrically independent of 3 and 4.

If the link between 2 and 3 is in place then there would be 230V at 2 all the time and this would be connected to 1 when the timer is on.

Thats magic, I understand that perfect now, thanks soo much for your help, I wish everybody was like you in this day and age. Thanks again
 
I thought you understood after I explained! Never mind, I fell asleep after a few too many gin & bitter lemons. How did you get on today?
 
I thought you understood after I explained! Never mind, I fell asleep after a few too many gin & bitter lemons. How did you get on today?
Yea i was just overthinking things stroppy sorry, yea it turned out the timer was at fault here. But thanks for your help though :)
 