Quick one are boss in his wisdom orders 4core 6mm swa to supply an out door air con unit via an isolator why I don't no trying to terminate in to a 32a isolator was extremely tight my question is are you allowed to down size the cable from the isolator or would ou have to still youse the same cable size
 
6mm into 32Amp T/P isolator should be no probs so no need to be thinking about reducing outgoing csa surely?
 
I've done loads of 6mm into an isolator and 10mm. Don't think I could go above that with the isolators we use though. As long as the down sized cable can carry the design current then there shouldn't be a problem.
 
4mm could carry 32A safely providing ref method was OK, however I would go with post above!
Think of the storage heater situation 2.5/1.5 T+E to 1.5/1.5 flex
 
Quick one are boss in his wisdom orders 4core 6mm swa to supply an out door air con unit via an isolator why I don't no trying to terminate in to a 32a isolator was extremely tight my question is are you allowed to down size the cable from the isolator or would ou have to still youse the same cable size
we made the mistake of running 16mm 4 core SWA into a 32A isolator* the other week, by all accounts that was a proper git to fit. 6mm2 shouldn't be an issue really.



*solar on a farm as part of a 250m total AC cable run, so needed to be that size cable to keep the impedance within limits, we just didn't think properly about getting that in to the 32amp isolator.
 
Thanks for advice guys yes a bigger isolator would have been better but we didn't have one the out door unit only requires 20a supply just a moan could of used smaller cable wasn't sure you could down rate cable size always thought it was bad electrical practise so really what your saying is I could off used 2.5 swa from isolator to out door unit as its on a 20a breaker does this not break any reqs
 
Thanks for advice guys yes a bigger isolator would have been better but we didn't have one the out door unit only requires 20a supply just a moan could of used smaller cable wasn't sure you could down rate cable size always thought it was bad electrical practise so really what your saying is I could off used 2.5 swa from isolator to out door unit as its on a 20a breaker does this not break any reqs

Yes, that's correct

As long as the over current device is suitable for the smallest sized cable you will be fine
 