Just a note for engineer 54, it doesnt half to be an earth rod to make it TT,any permenently fixed earth source will suffice.
So long as it meets the requirements of an electrical permanent electrode you'd be right. Such a suitable electrode would be for instance a Ufer earth, or say a steel building where the steel posts have been driven or concreted into the ground.
What isn't acceptable, is the use of extraneous service pipes that can be replaced by plastic service pipe at any time. It is also not generally permissable to use metallic service pipes, as the sole means of earthing to an electrical installation. So even in this case, it cannot be deemed a TT system!!
Aye ye are ................... for a Tyke ;)
i mean it would of course depend on the individual scenareo...
now, if we hadn`t been on that site every day for the time it took for the DNO to sort out a PME...i would of course not left it like it was..
but the first thing i did before anything else was get a Ze ..just to confirm there was actually an earth at the property (church)...and as i found it to be suitably low...i made the concious decision to leave it as is until the PME was done...
now if it was a case of just being there for ...say a couple of days..well, theres a different matter completely and a temporary rod would have been installed
Yes, of course Glen .... we believe you !! :wink_smile:
When I tested my home installation a few weeks ago out of curiousity I found the Ra to be fairly pants (by which I mean 'not good', not a pair of pants buried and connected to the earthing conductor, like GlennSparks tractor engine) around 120 ohms, but with all the bonding (gas and water) and the bent copper pipe with an earth connected to it, I got 0.something ohms instead. I know technically I should try to get the twig itself a bit better, but with a reading like that I'm not sure I'll bother! One day I will test the bent copper pipe that is hammered into the ground under the house on its own and see what reading that gives.
Your down to less than an ohm on your bonded pipe work?? lol!! Sorry i find that extremely hard to believe, in fact i'll go as far as saying, i don't believe it!!!!!!! So why is your earth rod only giving you an Ra of 120 ohms??
New posts
Reply to no earth in the UK Electrical Forum area at ElectriciansForums.net
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...