Discuss Block of flats. Max Demand in the UK Electrical Forum area at ElectriciansForums.net
bartkusal
Wonder if I can get some guidance, on max demand in block of flats. It always was hard for me as it always comes to massive demands, and I red here that it all comes with years of experience and that it is like an art. This is first bigger project I am taking on. So please don’t shoot.
I need to determine the max demand for the job, so the correct supply can be brought in.
Basically it is an old mansion being converted to a block of 11 flats.
Each flat will have: 2 lighting, 2 ring, 1 shower 8.5kW (37A), 1 cooker 4.5 kW (19.6A).
Option 1: Going by OSG diversity: 4A lights+4A lights+32A ring+8A ring+37A shower+16A cooker=101A (crazy)
Option 2: Going by 0.4 factor diversity: (6+6+32+32+37+19.6) x 0.4 =53A (more like it)
For the whole house:
Can I treat flats as circuits in this instance and apply 0.4 factor again? Then:
Option 1: ((101A x 11)+ 20A landlords board) x 0.4 =452A (3Ph), Supply current per phase 452/3=150A. So I need then 103.5kW 3ph+N supply.
Option 2: ((53A x11) +20A landlord board) x 0.4 = 241A (3ph). Supply current per phase 241/3=80A. So I need then 55.2kW 3ph+N supply.
I find myself thinking to come up with Option 3, :banghead:: (option 1+ option2) /2. =80kw 3ph + N supply.
So what you think? Am I somewhere near with my thinking? Obviously if I can’t work it out I will go with safest but unfortunately most expensive option 1, it just seems it will be rather large supply cable 50 mm2 or maybe higher, it is what it is I suppose. Not sure about ratings on supply cables, just had a look in regs book, 50mm2=135A and 70mm2=167A, SWA XLPE reference D, obviously its different cable.
After and if I will get this confirmed by more experienced, I then will share with my calcs and plans of action for the customer’s installation.
Thanks in advance for your help and guidance.
Al
How many rooms in each flat to require 2 ring finals? I'd doubt very much that you'd be pulling 32a on the 2nd circuit? Would need some idea of loading in each flat not just the circuits.
On option 1 , second ring was calculated as 25%, I think that what it says in OSG if i remember exactly.
I quickly drafted my OP from the top of my head, and have to go now and do some work will be back in the evening to read all the replies, thanks again.
Max Demand & Diversity = Nightmare!
A case study (my house)
3 bed detached, me, wife & 3 daughters.
80A Cutout Fuse
3 RFCs
2 Lights
1 Smokes
No electric shower or electric heating.
Computer, TV, Hifi, Fridge/Freezer, Lights all active for 10 hours.
Combiboiler, Washing machine & dishwasher now and again.
I'm using about 75kWh a week @ 13.4p/kWh
So, on average, over 10 hours usage/day...
75/7 = 10.7kWh/day
10.7/10 = 1.07kW
1.07/230 = 4.4 Amps (AVERAGE)
So, apart from 10A spikes (very often) from the kettle, the whole house is pulling sod all.
I hope that's right, please correct me if it's not!!! :smilielol5:
To follow on from Archy’s post.
Like Archy gas heating and cooking. I have an electric shower but I like a bath, so gas again.
A fridge/freezer and a freezer. The kettle gets some hammer, microwave used occasionally.
No one will live with me! (Not if they’ve got any bloody sense).
I re-jigged the CU for my flat. Everything running through a 16A RCBO. Never tripped for the trial period of a fortnight.
The stupid thing is the biggest power users in my flat are the PC’s. If I’m at home and awake they are on.
Hello, thanks for replies. Yes I do understand what you Tony and Archy are saying, it’s easy to say when you know exactly what you use and how much.
In my instance I needto design an adequate system, where I don’t know the exact load, what I knew I did put it in the OP. What I know, is that it’s going to be 11 modern flats done up for sale or for rent, so I don’t know who and how many people living in them, or what they likely activities and patterns of usage. Kitchen will have all the modern appliance’s imaginable built in.
I think I would be safe to go with option 3 or there bouts, what you guys think. I know it will be ok, its just that I lack confidance, I think?
I would tend to look at this from a practical point of view considering the capability of fuses to take over current.
In general you could consider on average a house may take about 15A, this is considering multiple users in different houses using power simultaneously. For a flat this would be reduced to maybe 10A to use as an average.
For each flat in your situation lighting can be discounted because it will add very little to the overall loading (comparatively).
You normal socket circuits may take on average 5A considering 11 flats and multiple usage it is probably somewhere close.
Kitchen circuits would be likely to take more because of high power appliances and usage of kettles / toasters in the morning could be simultaneous between flats. So there may be a peak here but only for maybe ten minutes. So say take this as 15A.
Showers will take a high peak and may be on simultaneously and for on average say about 20 mins so you need to account for a 35A loading for a short while.
Cooker again could be on simultaneously across flats but diversity level of 16A should be OK.
So you are looking at 36A per flat with a twenty minute 100% overload so a 40A fuse would handle this but be a bit close to the wire. However you are averaging out across the flats and so a 40A demand for each individual flat should be OK to consider as an average ( I would tend to use a 60A protection for each flat just in case).
Therefore you are looking at say 10kW per flat the split would be 4, 4, 3+landlord so each phase would need 40kW or 170A.
This is all just estimates and guesswork but comes out similar to your option two, I would have thought from a basic set up that this should be OK.
However this is in no way a professional assessment so you would need to make your own judgement on what is required.
Reply to Block of flats. Max Demand in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Hi all, I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply. What...
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...