S
sparks72
Went to a job yesterday,
woman has had electric underfloor heating installed last year in her bathroom,
no certification, on a 50 amp mcb on the RCD side of the CU, installer had used the old 10mm shower cable
& jointboxed it to a 2.5 mm T&E to a switched fused spur!
Installer has dissapeared into thin air as usual (I reckon her partner did it)
but he's tight staying tight lipped!
She doesn't want a new feed installing as I advised,
anyone have any ideas of what can be done to tidy up this mess :confused:
Thanks in advance.
Nothing wrong with what you have described, although the 2.5 feeding the spur should really be 10mm also.
However, you could drop the MCB to a 16 or 20A
Thanks but 10mm is way to big!
the cable going to the heating mat is 2.5mm,
I agree with reducing the MCB to 16amp but what about voltage drop?
4mm on a 16 amp mcb would have been fine,
will change the 2.5mm to 4mm or 6mm me thinks, oh well, another day another mess!
Install a spur on a deep surface box where the JB is. Then downsize to your 2.5. I know for a fact a 10mm can be terminated in an MK spur, but you'll have issues dressing it in a 25mm patress hence the deep box.
Hi,
Is there a big problem with what you have described as whats the max current that will be pulled down the 10mm & 2.5 to fsu. Fused at 3A for heat mat ?? Bit rough but not a problem i dont think. Prob get shot down tho now .... hardhat on :)
Hi,
Potentially a 50A fault current through the 2.5.
Thanks guys,
Eggster71, I was worried about the 10mm not fitting in a sfs, haven't used MK for a while,
I'ts a plasterboard wall so getting a deep box in isn't a problem. :D
and??
what you want to look at is the rating and response time of your protective devices,
2.5mm cable will handle many hundreds of thousands of amperes (never mind 50), for a short period.
this is what IET 17ED Tables are for
and??
So you'd run a 2.5 off a 50A mcb and walk away would you?
yes,my friend, work out the load and calculate accordingly, a 100Amp breaker, no doubt protects your house, is your house wired 25mm SQ copper??? doubt it.
No, my house is supplied by 25mm tails which are protected by a 100A fuselink and terminated into a mainswitch rated at safe for 100A isolation. The final circuits are protected by individual MCBs each one rated below the stated maximum rating of the cables used. I did not calculate those given ratings, someone a great deal wiser did. I am not about to argue how they came to those figures as I don't know. However, I have in the past gone to jobs where a loose connection has caused an arc, this has in turn taken out the MCB. I wouldn't like to think I'd left the potential of a 50A fault on a 2.5 rated at somewhere in the region of 20A. If the wiring was in metal trunking as in an industrial set up running to a device to limit the draw then I'd have less of a problem with it. As it stands, in a domestic situation, (I'm guessing in a airing cupboard where it is quite possibly going to be buried under clothes/ towels etc) there is no way I would not take an extra half an hour and a few quid's worth of spur to make sure that the 2.5 had adequate protection!
And breathe..........
No offence dude, but I'd always prefer to cover my ---! ;)
good points, all correct and i agree, i,m industrial and just had a different take on the question.
by the way, power=volts*amps as im sure you know, thats how i decide on protection rating, and like you said , err on the side of caution.
and??
What i'm trying to put across is that the installation has been botched from the start,
I've been asked to sort it out, a 10mm cable to a 2.5mm that's Jointed under the floor
isn't good practice for a start, I couldn't care if it's supplied with a 185mm SWA as long as its
done correctly ;)
BTW, got on to the underfloor heating manafucturer, they ask for a 16 amp MCB.
What i'm trying to put acroos is that the installation has been botched from the start,
done correctly ;)
Happy days then, lob out the 50A sling in a 16A, chuck the 10mm and 2.5 in a 20A switch and everyone's a winner! :)