O

obleo

Hi all. I am wiring a 2 port motorised valve and would value advice re. wiring of aux. switch.
Instead of having a permanent feed on orange (or grey) wire, could I loop a feed from the valve motor, that is to say, use the "feed" from the programmer that energises the motorised valve to feed one side of the aux. switch? Reason being that when the aux. switch fails (as it will) the boiler will not remain on as there is no permanent feed.
 
If you do that you will get a backfeed from any other valve in the system so that it remains open as long as any other valve is energised.

This is the reason they started putting switches in them in the first place.

Also the convention is to put the perm live on the grey and the orange is the switched live to the boiler. Keeps it closer in line with other types of valve then.
 
Why would the aux fail ?? I've installed lots of valves and have yet to have a faulty aux . I take it that ur saying that the aux switch will fail in the closed position ? Surely the valve will be controlled via either room stat or tank stat , I think you should wire it in the conventional manor , sure you could work it the way you've mentioned like was previously mentioned if aux failed in the closed position surely if there were another zone valve installed then it would still open the valve in question not eliminating you're query
 
The aux. switch mostly does not fail "as such". Worn valves may not move (switch) the aux. switch on opening or closing.
 
They do fail occasionally, but i've only ever had them fail open circuit, never seen one fail closed.<br><br>Far more regular is the damned motors failing in them
 
Aindowsimon. Yes I meant the switched feed from the 'stat.
I had thought that if the boiler was energised from another valve, the backfeed would go to the dead side of the aux. switch in another valve regardless of where it takes its source of supply.
 
The boiler cannot remain on if the feed from the 'stat is removed i.e. if the programmer switches off, as there is no premanent feed to aux. switch.
 
I realy havnt had this problem often enough for me to consider altering the wiring ? I understand things fail from time to time Maybe your experiences are different have some faith make sure you get quality reputable manufacturer of materials
 

Reply to Motorised valve 2 port in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
1K
I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
Hi there, the heating system I am working on has 6 zones and valves for each zone which was working fine with one boiler and one pump. some rads...
Replies
1
Views
1K
I recently wired a heating system with a UFH8 manifold and an unvented cylinder.... easy. Well it threw up a few problems. Initially I had the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock