Hi there, the heating system I am working on has 6 zones and valves for each zone which was working fine with one boiler and one pump. some rads weren't getting hot so the plumber has installed 2 x pumps, one for 3 zones and another for 3 zones, the problem is I originally had all the oranges from the valves connected to the switch live to boiler and the pump. obviously now I need to somehow split the oranges to feed the appropriate pumps while keeping the single switch live to the boiler from both. I presume I need a relay for this but I have no experience with relays and am stuck as to how to wire them. I have an imo RL01C 8 pin 2 c/o relay but don't know how to wire it.
any help greatly appreciated
 
You will need 2x 8 pin relays, one for each pump.

For each set of 3 valves:
Connect the coil to the orange of the relevant valves.
Connect a permanent live to both commons.
Connect the pump to one of the N/O contacts.
The other N/O contact will be your switched live to the boiler.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Oxfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
2 pumps on one system
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
1

Thread Tags

Advert

Thread statistics

Created
Phil2552,
Last reply from
davesparks,
Replies
1
Views
1,335

Advert